Banging radiators - Again I know it's been beat to death...
faster340
Member Posts: 6
I have one radiator fiercely bangs. It's a one pipe steam system. The radiators that don't bang I hear the valves hissing when it's making heat. The radiator that does bang I don't hear the valve hissing. Could this be a bad valve causing the banging because it can't release pressure? The radiator has been tilted towards the valve numerous times and at numerous heights.
Thanks.
Thanks.
0
Comments
-
Piping
Have you tried swapping air vents with another radiator?
Make sure the pipes that feed this radiator are sloped properly so water can drain back to the steam main and make sure the slope on the steam main is ok.
If none of that works try removing the vent on the radiator and see if any air is coming out of the vent tapping. Do this when the boiler firs comes on and the system is not steam hot.
Put that air vent back on when the test is done.
If you get no air coming out as the system begins to produce steam your input radiator valve might be stuck closed, not letting any steam in. I don't see why that would cause hammering without any trapped water in the main or at the start of the radiator feed pipe where it comes off the main.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
suggestions
Thanks. I will look into your suggestions...0 -
quite likely...
the floor valve is not fully open (even if fully turned open)..you may need to take it apart or replace with an new one or elbow..it could also me that your supply pooping is too small.
certainly easy test its to swap air vents between good and bad rads...more involved to working on the supply end.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
quite likely...
it's open all the way. I will swap air vents and see how that goes. Thanks.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements