Hello- this is a first time post / question. We recently completed a small addition of our home. The GC and plumbing sub added 2 new radiators to the system. The boiler is an older hydrotherm steam boiler. After restarting the heat, the boiler now cycles off every minute or so. You can see the water level drop in the glass and then the boiler shuts down. The water level rises again and the boiler re-fires. The plumber tried a number of things and nothing worked. He has settled on the idea that the equalizer was piped incorrectly during the original installation (and there should be only 1 hartford loop not 2). Does this seem right? Do the photos help? The plumber also turned off the 2 new radiators but the boiler continued to cycle on and off. We've owned this house for several years and the heat was working well before the work. Overall the experience has been great- I just a little nervous, given the back and forth, about moving forward.
thanks for any help!
fulton
thanks for any help!
fulton
0
Comments
-
dirty water perhaps ...
with the addition of the new rads came also the addition of new pipes, iron and oil .. and likely, your water suffered .. do a few proper skims, maybe even a full drain and flush .. it's likely your water as the first culprit .. since everything was dandy before adding all the new contaminants. and it could take quite a while to clean the system off all the new, not even visible to you, oil and particles.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
has pressure changed?
inadvertent changes in the operating pressure could also make an unsteady waterline, as the water level in the returns can move up 1.75 inches for each ounce of system pressure! unfortunately the standard 0-30 psi gauge is useless for this diagnostic work. try getting a 0-3 psi gauge [gaugestore.com] and put that on the same pigtail as the pressuretrol [clean the pigtail], and then you will see if you are above 1.5 psi.--nbc0 -
dare I ask ..
why there is a pipe with a pall valve on your pressure relief valve .. perhaps this is for attempted skimming?1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
steam system - equalizer question
Not sure - as the plumber describes the problem - the boiler can not build up enough pressure because it is drawing out the water - this is due to the incorrect installation of the equalizer...0 -
the return piping
is wrong, what else did they mess with? dirty water from the cutting oil. Skim it or add approve cleaner ands drain and flush.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
steam system - equalizer question
yes - for attempted skimming0 -
Thats not how you
Skim a boiler. Thats how you coat the top inside of a boiler with oil and let it drip back down as it runs later.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
steam system - equalizer question
The return piping is as it was installed originally.
So far they have added a "skimmer" valve, replaced the main air vent and tried a skimming.0 -
steam system - equalizer question
Will you explain this comment a little more!\? Thanks for your help!0 -
as charlie said .. and as I alluded to ...
you can't skim via a small hole at the top of a vessel .. as charlie mentioned .. all that will do is raise the muck up until finally all the muck touches to ceiling of the boiler .. and one little bit of muck will come out the hole and the water will keep flowing out that one little cleared hole .. then when you are done .. you drop the water level back down and all the muck is not stuck to the ceiling .. and once you begin making steam .. all that muck ends up back on top of the water ..
you need to skim from a side opening .. so that the muck is able to float on top of the water and find it's way out the side .. once the muck has touched the ceiling it's game over ..1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
steam system - equalizer question
thanks - i'll verify with the GC - i'm fairly sure that it was skimmed from there
should the pipe and the pall valve be removed?0 -
steam system - equalizer question
thanks again for all the posts0 -
i think...
you probably should remove the pipe and valve from beneath the steam relief safety .. if nothing else .. someone may open the valve (accidentally or otherwise) while the system is running and you will have a boiler room full of steam in a hurry. and it probably violates some code about messing with the steam safety relief system.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Equalizer still all wrong!
I cant see by the capped fitting on the return side, that something has been recently modified. I don't know how bad it was before, but the piping is still ALL WRONG!
The equalizer should not drop to the floor and then turn back up to the return tapping of the boiler.
Also, the header should be traveling horizontally where the steam connection of the building connects off the top.
Let me see if I can find a manual for this boiler online. If I do, I will add it to this reply.
Found the manual.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
steam system - equalizer question
thanks that was very helpful
it seems like the plumber's diagnosis of the problems with the return side is correct
i'll discuss with him the skimming process
any thoughts on why it worked well before and cycles on and off now - even with the 2 new rad's taken off? could it just be the oily / dirty water?
would a good strategy be to first have is properly skimmed and flushed - then recheck before addressing the work on the return side?0 -
yes dirty water..
should be addressed first .. as you said, everything was dandy before the added rads .. as pointed out, there are a few other issues, but address your water first .. if it's really causing problems, try running a bit overfilled to limit the constant LWCO cycling.
i'm not sure how you will perform a proper skim on that boiler .. perhaps there is a skim port lurking beneath the jacket, but I wouldn't go trying to get it open.
flush, fill, boil repeat .. maybe stick a hose in the top opening where your pressure relief valve is with the boiler drains open to try to clean out the inside. maybe he can pull the DHW coil, but I would recommend that necessarily either .. you may open up all kinds of other trouble.
anytime you add significant amounts of fresh new water, boil it immediately for 10mins to drive off dissolve oxygen which will rust out your boiler.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements