Riello oil burner re-set button

brr_chilly
Member Posts: 1
in Oil Heating
Hi boys, I have a 3 year old Riello oil burner. The fan is blowing but no heat. When I hit the red reset button, it tries to start, then puts out. Red light comes back on. Plenty of oil. $600 worth (ugh) delivered this week & never ran out. What can cause the reset button to not work? Husband is away traveling and I am very cold :)
0
Comments
-
There are a host of things that can cause this.
Most of them need to be diagnosed and addressed onsite. I would recommend that you call your heating guy. If you didn't run out of oil then it is probably something with the burner. Riello's are tanks, but a fouled nozzle or plugged strainer or filter could be the cause.
Time to call a pro on this one.0