We can not get any heat up to the 2nd floor radiators.  We replaced the main vents on the returns.  We have a 10 year old Burnham oil steam boiler.  It is a one pipe system with heavy asbestos insulation and some of the insulation is missing.  The main is hot all the way around.  The 1" line that goes to the second floor is warm only about 2" off of the main.  The pressure gauge on the boiler never seems to come off of "0".  The pressuretrol setting seems to be at 1 psi.

Comments

  • jpf321
    jpf321 Member Posts: 1,568
    have a look at...

    this radiator NO-HEAT troubleshooting list .. and then report back...

    http://www.heatinghelp.com/forum-thread/129206/Radiator-not-getting-any-heat#p1185051
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • Rod
    Rod Posts: 2,067
    Radiator Problems

    Hi- Welcome to the steam section. We'll need to ask you a few questions so we can get a better understanding of your steam system. As i mentioned on the main "Wall", "Was your steam system operating well in the past? If so what has been

    changes since then?"  Have you had the boiler cleaned and the burner adjusted recently?  What are the model of the vents you installed on the radiators?



    - Rod
  • daneheat
    daneheat Member Posts: 8
    Vents that were replaced

    The main vents that we replaced are Hoffman Specialty 75 Steam Vents 1/2 x 3/4- 2 of them

    On the Radiators we installed a couple of Dole 1A Vari- Vent air valve 1/8" angle and a couple of Legend model T-60 steam air vent 1/8" angle vents

    The boiler is clean and working properly.   We just started servicing this boiler about a year ago, so I don't know if it worked before or not.
  • Rod
    Rod Posts: 2,067
    edited January 2011
    Try another vent?

    As a general rule you should stick to the same model radiator vents. I'm not familiar with the Legend T-60 as it isn't a standard steam radiator vent. Most of the Legend vents (T-75) I know of are for HW.  Are these T-60 s on the problem radiators? if so I'd change it over to one of the Doles.

    - Rod