New Year, New Boiler!
Steamhead
Member Posts: 17,312
Another atmospheric with a hole above the waterline. This could be habit-forming.....
This system is counterflow, and may have originally run its condensate straight back into the original boiler's steam outlet. We removed a 2"x2"x3" bullhead tee that was feeding steam into both mains, and it looks like the drip lines were added sometime after the system was first installed.
This system is counterflow, and may have originally run its condensate straight back into the original boiler's steam outlet. We removed a 2"x2"x3" bullhead tee that was feeding steam into both mains, and it looks like the drip lines were added sometime after the system was first installed.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
We installed a Slant/Fin Intrepid this time
since it fit the available space better than the Smith G-8 would have. Burner is the Carlin EZ-Gas. Gordon's piping artistry can be seen on the drip-line manifold.
The owners are planning an addition, and if built we will heat it with steam. We left a 2" tee in the short steam main for this, and there's room to tie in another drip line. The boiler is big enough to handle the addition, and is down-fired in its present state. Still had good combustion numbers though!
Happy New Year all- keep steaming!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Nice looking job on the replacement.
As always, well done! Now thats one heck of a hole in that section..crap, you could put a baseball thru that gap...were they taking on lots of water??gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Not recently that I know of
the VXT will tell us for sure. We've worked on this system a few times, but I haven't gotten around to pulling the file on it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
as usual
Nice work steam0 -
Nice Job!
Nice looking installation! I was just wondering , How thick is the boiler wall normally at the point where it corroded through? Do they all corrode through in the same area?
- Rod0 -
I think
it's 1/8" or 3/16", not exactly sure, Maybe I'll have time to check before sending it to China.
This one and the one before did corrode in almost exactly the same place.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Rot Hole
That boiler looks to be a Burnham Independence. Just like the other one you did. Burnham has extremely restrictive instructions for make-up water for the Independence. I have an IN-4 and the manual states no more than .1 gallons a month or 1 gallon a year. A similarly sized Megasteam is allowed 6 gallons a month. My system has no leaks that I can find and I lose about a 1/2 gallon a month. Before I add water I always flush sediment so I probably add 1gallon a month. Good thing I have a probe LWCO or I'd be adding even more water.0 -
Hmmmmmmmmm
have to ask about that. I didn't call out the brand, didn't want to look like I was bashing Burnham.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks
for the kind words!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements