Thermostatic rad. valves
ddlong1286@yahoo.com
Member Posts: 139
Putting in Danfoss RA-2000 rad. valves on cast iron radiators I took the manual valves off and installed the new thermo rad valves. I then noticed that I had installed them on the return side of the radiator. This is only on two of the radiators. There is an arrow for flow on the RA-2000, but am wondering if this will affect the operation of the valve that much?
Thanks
Don in MO
Thanks
Don in MO
0
Comments
-
In a word..... It depends!
If there is fast flow through the radiator, then yes, you will know when the TRV is close to shut off. It will start knocking as the needle is sucked into the seat of the valve and will sound like a jack hammer or wood pecker.
If the flow rate is not high (as in gravity circulation) , and the pressure drop through the radiators is low (BIG open water ways on everything), it will bypass and probably won't be a problem.
Don't be too hard on yourself. EVERYONE has put at least one in backwards :-)
METhere was an error rendering this rich post.
0 -
Danfoss valves in backwards
Mark is correct...it does make a difference and we have all done it.....my dad had a version of an old saying" "Happens to the best of them....and we just proved it"
I hope you get to hear the rattle it makes sometime. It's another one of those sounds that you will never forget and will make future troubleshooting so much easier. like the sound of a slipping burner coupling or the tic-tic of condensate dropping on a water heater burner.....sounds that get imbedded in your brain....0 -
Restrictor plates in Radiator
Thanks for the info. Talked to the home owner and explained the sitiuation and we are repiping so the TRV's are installed correctly.
So I took apart the union on the other side of the rad. and found a restritor plate. If I remember correctly they where used on gravity systems? Will I have a problem leaving them in the other radiators that don't need re-piped? Will I have a problem taking some out?
Thanks
Don in MO0 -
Restrictive orifi...
Were typically deployed on the upper floor radiators only. Occasionally you will find them on first floor rad's that were real close to the heat source, but rare. If you've got'em, pull'em.
The TRV's will work to balance out the flows based on demand.
METhere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements