Vents hiss loudly with new boiler
Barbara
Member Posts: 4
On our one-pipe steam system, we replaced a 60 year old oil-fired boiler with a gas-fired Peerless Series 63 cast iron boiler. The old boiler took forever to heat but did it quietly with no clangs, knocks, gurgles or vent hissing. The new boiler zooms the heat through the house in a few minutes (.5 -1.5 psi) with no clangs, knocks or gurgles but the vents hiss so loudly that they wake everyone up from sound sleep. The main is vented with a new Hoffman 4A quick vent (I don't know what was originally used). The room radiators are vented with Hoffman 1A vents set according to radiator size. We replaced the old Hoffmans with new ones, thinking that might help, but it didn't. Any suggestions or do we need to buy earplugs to get a good night's sleep in the deep cold of January?
Thanks
Thanks
0
Comments
-
Need more Main Venting
Hi- You need more main venting. . According to Gerry Gill's excellent venting chart, the Hoffman 4A vents .133 cu.ft /min , The Gorton # 1 vents .330 cu.ft /min and the Gorton #2 vents 1.100 cu.ft/min If you have room/clearnace I'd install a Gorton #2. The hissing is because the radiator vents have to vent all the air from the mains due to the present main vent (the 4A) being too small. Also you might want to check you boiler pressure . It should be operating at under 2 PSI.
- Rod0 -
How many feet
of mains do you have? This is the main pipe that loops around the basement. You may also have more than one loop. The suggestion of adding a Gorton #2 is what I would do but you may even need to add two or three of them in an 'antler' configuration.
Also are your pipes insulated?0 -
Vents hiss loudly with new boiler
90 feet of main, only one main loop, with 1.5" of fiberglass insulation (asbestos removed and replaced). I looked at Gill's chart and agree that a larger vent is needed by those calculations. Thanks - I'll try that and report back to the wall.0 -
can a main vent be TOO large?
We have 90 feet of 2 1/2" main loop, with 1 1/2' insulation. That's about 2.7 cubic feet of air to vent. The boiler seems to run about 2-3 minutes so a Gorton #2 seems appropriate. But can a main vent be TOO large?0 -
Main Vents
Hi- Generally you can't get into any trouble with "too much" venting on the main vents. Radiator vents are another story. Here's a link to Gerry Gill's website and his page on venting that might be of interest to you.You might want to take a look around his website. He has a lot of other intersting info there.
http://www.gwgillplumbingandheating.com/webapp/GetPage?pid=415
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements