Water Coming out From Vent

nycpa
nycpa Member Posts: 108
I've been having this problem with one of my radiators on the first floor.  Every time its 25 degrees or below outside, the boiler kicks in more but after a while water pours out of the vent from the radiator in the dining room.  This is the only radiator that leaks.  I changed the air vent like three times but this still happens.  The latest one is a Gorton.  I called the company and they told me 9 out of 10 times its the pitch of the radiator.  I changed the pitch by adding wood on the vent side of the legs and measured it with a level.  It still leaks.  I looked at my pressure cut in and its set at 3.  My next step is to change the valve and i am going to ask my plumber to snake the return valve.  Other than this, can you guys suggest something that I can do besides this or if something else might be causing this problem.  Thank You.  

Comments

  • kcopp
    kcopp Member Posts: 4,472
    Couple of things....

    -Turn down the pressure. 1/2 pound is all you should need.... 2 at the most.

    -Flush out your boiler... do this when it is not HOT.....Spitting vents happen a lot when the water in  the boiler is contaminated/ dirty. From what I see on the sight glass the water is filthy.

    -Check to see that the rad valve is all the way open.

    -insulate your mains.

    kpc
  • nycpa
    nycpa Member Posts: 108
    edited December 2010
    water coming from vent

    I tried adjusting the pressure reading but the cut in switch is stuck at 3. I cant move the switch up or down.   I just tried after the boiler came on.  Is this normal?  Do I have to change the cut in switch? 
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,372
    Piping is not great. they used

    sewer pipe fitting on the header. The copper is bad on its own but they have all that steam squeezing into a 1 1/2" pipe. The pressuretrol needs replaced if you can not turn that screw. I am wondering is it leaking internally causing the rust marks or is something dripping on it?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • jpf321
    jpf321 Member Posts: 1,568
    you must turn screw on top

    NOT just try to move"switch" with your fingers.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • nycpa
    nycpa Member Posts: 108
    Vent Water

    Thanks for your reply.  I don't really see any rust marks.  But I remember a plumber before telling me that they used the wrong copper to save money.  What is wrong with my pipes and what would be the correct ones?  Thanks for your help.
  • nycpa
    nycpa Member Posts: 108
    Pressure Reader

    Can you let me know if I should adjust my cut in pressure to 1/2.  I included a picture on the top.  That's the lowest it goes.  Thanks.
  • BobC
    BobC Member Posts: 5,502
    Adjustment

    Yes adjust that front tab with the screw on the top of the pressuretrol so it reads 0.5PSI, that's about as low as it will go. next remove the pressuretrols cover by loosening the screw on the front lower center and make sure the knob inside is set to 1. next double check the radiator input valve is open fully (turned max ccw)



    A steam boiler should be piped with threaded steel pipe anyplace above the waterline, copper is ok below the waterline.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • nycpa
    nycpa Member Posts: 108
    Valve

    The value that you refer you in the last part of your sentence, do you mean the valve that is connected to the actual radiator or another valve that is connected to the boiler.  If so, where in the boiler would it be located.   Thanks. 
  • jpf321
    jpf321 Member Posts: 1,568
    floor valve at radiator

    bob meant the valve near the radiator on the floor
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • nycpa
    nycpa Member Posts: 108
    edited December 2010
    Automatic Feed

    Thanks for all the help fellas.  I just had one more question.  I turned the cut in to .5 psi and the differential knob to 1.  I also drained out the water.  Now my automatic water feeder doesn't seem to work.  Its suppose to kick in after 10 minutes.  Its a VTX feeder.  It was working fine as of last week.  My LWCO works because the red light comes on. 



    Could changing the pressuretrol make my water feeder stop working?  I tried to reset the feeder and changed the time to 8 minutes but that failed. 



    Also, I was told that the header pipes of my boiler were not the proper ones.  Can you guys let me know what I need installed so I can tell my plumber.  Is it worth to change since the boiler worked fine for four years and its year of manufacture is 1983.  



    Thanks for all your help.   
  • BobC
    BobC Member Posts: 5,502
    Coincidence

    Adjusting the pressuretrol has nothing to do with the LWCO or the automatic water feeder, what ever happened was coincidental or else something got jostled along the way. It might be worth checking the electrical connections to make sure nothing is loose.



    You should not have to add water to a steam boiler more often than every 2-3 weeks, if it has to be added a lot more often you have a leak somewhere. All my steam boilers have had manual feed and I've had no problems for 40+ years and two houses.



    Your header should be threaded black steel but at 27 years old I don't know if I'd mess with that lest something go arwy while applying force with the big wrenches. You don't have to worry too much about the copper expansion because you only have the single boiler output pipe. One thing you should do is to insulate that header and any steam piping yo can with 1" pipe insulation, that will make a difference.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • nycpa
    nycpa Member Posts: 108
    Insulation of Header

    Thanks for your help Bob.  Can I insulate my headers with the fiberglass insulation they make for duct vents.  They are easy to apply around the pipes and I can cut them and tape them with foil tape.



    If not, I guess my other option is to buy specific 2 inch and I.5 inch tubes. 



    Now that I adjusted my pressuretrol, do you think I still need to call me plumber and ask him to change the Radiator valve and snake that radiators pipe.  It'll probably cost me like $300 or something like that. 
  • BobC
    BobC Member Posts: 5,502
    edited December 2010
    Pipe insulation.

    Any insulation should do as long as it's able to handle the temperature (215F) and it's thick enough, foam insulation won't work. Some duct insulation is pretty thin, it has to be at least an inch thick to have good results and as i said it can't be made of foam. Home Depot sells pipe insulation but it's only 1/2" thick so it's really not much good. I've seen people just wrap the pipe with 3" insulation; not pretty but that will work as long as you don't compress it too much.



    I'd give the lower a pressure a few days before having the plumber start to snake anything out.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • nycpa
    nycpa Member Posts: 108
    Radiator Didn't heat

    I changed me pressuretrol setting to a 1/2 today and the differential was at its usual setting of 1.  My radiators failed to heat.  I put the pressuretrol back to 2 because that was the last setting that worked.  Could my boiler be undersized?  What would cause my radiators not to heat up at 1/2 psi.  In the four years that I lived in the house, its been at 3 psi.  Thanks.  
  • Steamhead
    Steamhead Member Posts: 17,380
    Either the pressuretrol is bad

    or your air vents aren't doing their job. Time to call a pro, since pressure is a safety issue.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • nycpa
    nycpa Member Posts: 108
    Steam Specialist

    My air vents are all new Gortans.  I don' t think they would fail.  My Radiators work now that I increased the cut in to 2psi.  I live in Valley Stream, NY.  Is there anyone that specializes in steam heating that I can call for service.  My plumber isn't a Steam specialists but I think he should be able to change the pressuretrol if that's the problem.    
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    Use: Find a Contractor.

    Two in New Hyde Park, but they seem the same: Triple Crown.
  • BobC
    BobC Member Posts: 5,502
    Vents

    It seems strange that lowering the pressure would cause problems unless your system needs to be balanced. It's possible that lessening the vent rates of some radiators would coax the steam over to the radiator that's being starved.



    What vent are you using on each radiator in the heating system? I can see the one on the problem radiator is a Gorton, what model is it? Gorton makes great vents but it's a shame they don't make a variable vent.



    What are you using for main vents?
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • jpf321
    jpf321 Member Posts: 1,568
    I bank in valley stream...

    I'm happy to stop by this week for a wallie to wallie look see.contact me directly.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • nycpa
    nycpa Member Posts: 108
    Air Vents

    All the Air Vents are Gorton's Vapor Equalizing Valve V Number 5 no. 2709550.  The previous plumber I called to install these made some of the holes bigger in the valves such as in the living room and the master bedroom but they are all the same Gorton.  He seem to know a little about my Steam Boiler cause he did something a few years back to force out all the return water that sits in the return pipes.  That water looked like chocolate.  I am hesitant to call him because he charges $100 an hour and I had to pay for him coming late so he can smoke a cigarette.  My current plumber who I trust a lot doesn't seem to be a Steam specialist, last year when I had this problem he told me I put too much water in the boiler which I knew wasn't true because I drained my boiler ever week and know how much water is in there.



    I don't know what I have in my main vent because they guys that fixed the wall in the basement covered it up, so I would have to cut out the sheet rock.  I remember it was larger sizes one shaped like a cone. 



    I really appreciate the time you guys take to respond to my problem.  I guess I will have to hire someone but I don't want them to miss the problem.      
  • Question

    When you lowered your cut in to .5 and the differential to 1 did the boiler cycle off on pressure? If it did not cycle off on pressure than changing the cut in and differential would not have corrected your radiators.

    There was an error rendering this rich post.

  • nycpa
    nycpa Member Posts: 108
    Cycle Off

    What do you mean did the boiler cycle off?  When I changed the setting to 1/2 psi the boiler was off and it was off for a while like 3 hours.  Then I left the house and when I came home 6 hours later, my thermostat was set at 67 but the temperature was 62.  I turned the thermostat off, boiler off, reset the psi to 2 then turned everything on.  It took like 1 hr to for the house to warm up again to 67.
  • BobC
    BobC Member Posts: 5,502
    bad pressuretrol

    It sounds like your boiler never turned on at all after you changed the settings to 1/2 on the outside and 1 on the dial inside. that indicates your pressuretrol's spring is probably shot.



    i would replace that; it's not hard to do

    Remove two wires (shut power to boiler off and turn circuit breaker off) and remove wires from the pressurtrol. Unscrew the pressuretrol from the pigtail. Put some teflon tape on the pigtail and screw the new pressuretrol onto the pigtail (remove knockout first so you can get the wires into the new pressuretrol). Wire up the new pressuretrol like the old one, set the limits and your done.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • jpf321
    jpf321 Member Posts: 1,568
    perhaps you missed

    my post above. I'm happy to stop over this week for a look.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • nycpa
    nycpa Member Posts: 108
    Pressuretrol

    Thanks guys for all the answers. 



    Is there a good brand and model of a Pressuretrol that I can purchase or should I get the same honeywell I already have.  I have a Weil-McCain boiler. 