Low water cutoffs old and new
John Lenhart
Member Posts: 25
I haven't installed a steam boiler in a few years now and have a question. I was wondering about the new probe type low water cut offs. Most manufacturers don't even have the old McDonnell Miller LWCO's installed on the new units. Is it worth while to have both old and new installed as a redundent backup? Any responses will be appreciated.
0
Comments
-
redundancy
most boilers over a certain size, must have 2 lwco's, according to our local codes. if one of them is the traditional float type, then it will encourage the building owner to inspect the boiler as he is blowing down the lwco at least every other week. he will see the beginnings of potential problems during that time.
i am certainly happy to have the float type because of this!
while you are at it, why not give the customer the option of a vaporstat, and good low-pressure gauge [gaugestore.com 0-15 ounces], and put them on the same pigtail with the code required [but useless 0-30 psi] , and don't forget massive main venting on the returns, if equipped!--nbc0 -
Low water cutoffs old and new.
This is for a four section 450 sq ft of steam boiler. Natural gas fired. I should of put this in the previous post. So two low water cutoffs are required on large boilers. But are they a good idea for small residential boilers?0 -
I do not use
two LWCO's on residential boilers as seldom does the home owner want to pay the added costs. I think it is a good idea though.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
how many lwcos
on a small boiler, there may not be the extra tappings for a second lwco. but i would always choose the float type for my boiler, no matter how small, as it would force me to visit the boiler on a regular basis, and check everything.--nbc0 -
LWCO's
John-
It depends on your jurisdiction. Around my part of town (Chicago)-if you have a system larger than 400,000 btu's- you need two LWCO's. Smaller than that, one will suffice. However, my code does not necessarily translate to yours-just check your local code. Redundancy is good in my book-I don't think you can ever be too safe-especially with steam.
All the Best-
Will0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements