Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
L8124C Aquastat
mjtct
Member Posts: 1
in Oil Heating
The circulator relay on my Honeywell L8124C Aquastat is intermittently chattering while furnace is running. Do I need a new Aquastat or is some troubleshooting required?
TXs Mike
TXs Mike
0
Comments
-
I'd try
to disconnect the wires fro "T T" and jump it out. If it still chatters, than replace it, if not, go down the line to see what's tied into it. Zone valves, 1 thermostat, switching relays?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements