I am asking my plumbing contractor to switch out my presurtrol with a vaporstat and he is refusing saying that it will void the warrantee of the boiler and says that my vapor steam system should use a presutrol.
Are there any Burnham guys on here that can confirm this. I need to get this resolved today.
Are there any Burnham guys on here that can confirm this. I need to get this resolved today.
0
Comments
-
Just have him install a tee
and wire them in series. He is at ease and you have a vaporstat.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
He is wrong but why
argue it. It will give you a safety incase the vaporstat malfunctions anyways.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Sounds good to me
i can't believe that putting a vaporstat would void anything.0 -
Sounds good to me
0 -
Sounds good to me
0 -
Is there anything i came give to him.
I called Burnham but no word yet0 -
I woulddn't think it would
Void the warranty if you have the correct pressure relief valve installed and it is functional... A pressuretrol can fail just as easily as a vaporstat, but it is not common.0 -
Vaporstat haters?
There is absolutely no reason in the world (in Burnham's or otherwise) that you cannot use a vaporstat. A vaporstat offers far better control for low pressure applications. The standard pressuretrol is cheaper-that's pretty much it's selling point0 -
it would be great
If i could get a Burnham to say it's "Ok", my contractor is holding firm that it will void the manufacture warrantee.0 -
vaporstat
time to hire a differant contractor0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements