Gorton d on riser
acl10
Member Posts: 349
Can I put Gorton D valves on the risers coming out of the end of the main if the main doesnt have an airvent and there is no place to put one? Wil the Gorton ds hold up?
0
Comments
-
Main Vents
Hi- What sort of steam system do you have? You could also place them on the end of the dry returns.
- Rod0 -
1 pipe steam
1 pipe staem I dont want to put it on the return because it will make noise in the room the return is located in. Can I use Gorton ds?0 -
Gorton D's
We use Gorton D's on the risers in the bathrooms of a couple of the buildings we manage (There are no radiators in the bathroom, only the steam risers) We put one vent at the top of the steam risers on the fourth floor and they have worked for several years.0 -
I am puting it on riser near main
I want to put the Gorton D on the riser coming out of the main. It will be about 6 inches up from the main in order to vent the main. There are 2 risers at the end of the main and I want to vent both of them with Goprtod ds will that work? The main doesnt have a vent so essentialy this is to vent the main.0 -
Do all Gortons have the same guts?
Do all Gortons have the same guts?0 -
Better than nothing but
not quite the right thing to do. Can you drill and tap the main near the end? Well 18" back from the drop or less if need be and use an antler.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements