to repipe or not to repipe
stembo
Member Posts: 9
We have a 1 pipe steam system in our home that delivers wonderful heat. It has been pretty reliable and reasonably quiet.
Despite that it seems to be running well, I know the near boiler piping is all wrong. It does seem to be hard to keep the boiler clean, and I doubt it is running as efficiently as it can. The boiler is a 7 year old EG-45 Weil Mclain that was installed by our gas company, and they simply did not follow the manufacturer's guidelines. Can anyone help me decide if I should bite the bullet and repipe the boiler next spring, or not?
The installer put in two 2" risers coming out of the boiler instead of one 2.5". There are 3 primary problems that I know of: 1) the header is 2" instead of the required 2.5" minimum; 2) the two risers coming out of the header are between the two risers coming out of the boiler, and 3) the first 24" of the risers laving the header are copper (the header and the piping from the boilerto it are all steel).
2 pics are attached. Everything is insulated very well, but I think you can get the jist of things.
Hope you all can help. At least we are nice and warm.
pq
Despite that it seems to be running well, I know the near boiler piping is all wrong. It does seem to be hard to keep the boiler clean, and I doubt it is running as efficiently as it can. The boiler is a 7 year old EG-45 Weil Mclain that was installed by our gas company, and they simply did not follow the manufacturer's guidelines. Can anyone help me decide if I should bite the bullet and repipe the boiler next spring, or not?
The installer put in two 2" risers coming out of the boiler instead of one 2.5". There are 3 primary problems that I know of: 1) the header is 2" instead of the required 2.5" minimum; 2) the two risers coming out of the header are between the two risers coming out of the boiler, and 3) the first 24" of the risers laving the header are copper (the header and the piping from the boilerto it are all steel).
2 pics are attached. Everything is insulated very well, but I think you can get the jist of things.
Hope you all can help. At least we are nice and warm.
pq
0
Comments
-
please delete this thread .. it is a dupe
simply Edit your post and put in the word "deleted".1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
deleted
deleted0 -
deleted
deleted0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements