Concept: Humidification from Steam System?
BobL
Member Posts: 1
This may be a poor idea, but the only dumb question is the one you don't ask .. In theory, could you just "donate" steam from the system somehow to achieve humidification?
With a steam system (single-pipe in my case), the steam's already in every room. Once the system heats, would it not be possible to have a humistatically-controlled opening in each room donate a bit of steam to the room as a source of humidification? In essence, are not all of our steam systems already geared to serve as whole-hose humidification with the right enhancement?
So theory to practice, does anyone know of such a humistatically-controled valve that could serve this purpose? Ideally, it would be timed to humidify only after the home has been brought up to an adequate heating level.
One issue I see is if additives are used in your steam circuit .. probably don't want to breathe those boiled off. Any eco-safe additives or MSDS info we could refer to in choosing the best additives compatible with this concept?
What other pros/cons can you see of this concept? Is boiler-generated steam less cost effective for humidification somehow?
Has this been done before? Any references or experiences with this approach?
Thanks,
BobL
With a steam system (single-pipe in my case), the steam's already in every room. Once the system heats, would it not be possible to have a humistatically-controlled opening in each room donate a bit of steam to the room as a source of humidification? In essence, are not all of our steam systems already geared to serve as whole-hose humidification with the right enhancement?
So theory to practice, does anyone know of such a humistatically-controled valve that could serve this purpose? Ideally, it would be timed to humidify only after the home has been brought up to an adequate heating level.
One issue I see is if additives are used in your steam circuit .. probably don't want to breathe those boiled off. Any eco-safe additives or MSDS info we could refer to in choosing the best additives compatible with this concept?
What other pros/cons can you see of this concept? Is boiler-generated steam less cost effective for humidification somehow?
Has this been done before? Any references or experiences with this approach?
Thanks,
BobL
0
Comments
-
Not a New Concept
Dri-Steam and Armstrong have been producing such products for commercial / institutional application for many years. Here are 2 links. http://www.dristeem.com/products_boilerSteam.jsp
http://www.armstronginternational.com/humidification-conditioned-steam
These systems are intended for boiler applications where there is a maintained boiler pressure at all times.
In such commercial systems there are many considerations that must be dealt with that make the concept completely innapropriate for residential and small commercial application.
If you lose either condensate or steam from a system, it must be replaced by makeup water. This will cause the total dissolved solids (hardness) and the chloride levels of the boiler water to increase. The levels of these two items must be very carefully regulated, through the use of controlled skimming and blowdown. Daily chemical analysis of the boiler water is critical to keeping a boiler operating in this manner within the proper parameters.
The bottom line is, while your theory is correct, you do already have steam, and steam can be used to humidfy living spaces....... DON'T DO IT!Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Low Tech Steam Humidifier
Hi- Not sure if this was just an engineering question or whether you were looking for a solution to low humidity. Here's a low tech solution: http://kilian.stores.yahoo.net/radhum.html
If you have kids, I'd tape the edges as they can be a bit on the sharp side.
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements