Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
low water cut off

Moshe
Member Posts: 5
Hello everyone:)
I am adding a backup low water cut off on my steam boiler. I mistakenly bought the Mcdonnell & Miller guard dog model # RB-122E which is made for a hot water system.
Quaestion is do i have to return it or can i use it anyway?
I am adding a backup low water cut off on my steam boiler. I mistakenly bought the Mcdonnell & Miller guard dog model # RB-122E which is made for a hot water system.
Quaestion is do i have to return it or can i use it anyway?
0
Comments
-
Return it
it won't last if used on a steam boiler.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements