setting the difference setpoint controller
ecletrical
in Solar
I'm pumping from 8 flat plates into a 1500 sq ft slab - no heat exchanger (there is diversion to an indirect should the temp go to high). I'd like suggestions on setting the delta t target to start pumping considering the massive size of the "heat exchanger" (tubing to concrete)
Is there any tank
in the circuit between the collectors and heat loops? Where is sensor 2 located?
The default setting on solar controllers is often 12 on 8 off. They are adjustable of course, but you want to prevent short cycling so it is a balancing act.
Also, most of the newer solar controls have variable speed functions, that can help with the cycling and might allow you to tighten up the on/ off settings.
I don't know that there is an ideal, one size fits all, setting, ideally you would have a data logger to record the operation of the system, watching the pump cycles, temperature swings, etc after you make adjustments.
hrBob "hot rod" Rohr
Living the hydronic dream0 -
no tank
no tank between collector and heat loops - directly into slab. However there is a 2nd circ which pumps to an indirect - this diverts flow to the tank based on the temperature of the supply line from the collector, etc.(the two circulators never operate at the same time). Otherwise it always goes to the slab. To answer your question - the 2nd sensor is in the tank, no sensor in the slab. The slab will never over heat. When the heating season is over a switch will divert all flow to the tank.
The tank will be kept at some minimum temp during the heating season - say 42F, after that all heat will go to the slab. This is not a temperature controlled space - it is an equipment shed for a dairy farm; the purpose to minimize condensation on equipment.
Thanks for the suggestion, I will datalog cycling. Then maybe I can fine tune.0 -
add a sensor in the slab
If you can still do it, I'd add a sensor in the slab as S2 and then probably just use the delta's that Rod suggested (12 and 8).
If the pipe run from the collectors is very long, maybe wind them up to 17 and 12 or something like that.
Finally, if your controller supports variable speed pumping, I'd definitely enable it here. When pumping to a low temperature load (like a direct slab is likely to be), we find variable speed control extends the solar day by close to an hour at each end compared to a fixed speed pump which is optimized for the high insolation periods.
best of luck
~Fortunat