Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
venting capacity of 1/8"?
jpf321
Member Posts: 1,568
does anyone know the venting capacity of 1/8" pipe? thanks. i know 1/2" = about 8 gorton #1's. and 1/2" has internal area of 0.196 vs 1/8" with internal area of 0.012
is my math the correct when i say that 0.012/0.196 = 0.06 or 6% and therefore 1/8" = about 6% of 8vents = 0.48 gorton #1's? that doesn't make any sense .. since a Gorton 1 = a gorton D and we have gorton Ds on 1/8" all the time,
is my math the correct when i say that 0.012/0.196 = 0.06 or 6% and therefore 1/8" = about 6% of 8vents = 0.48 gorton #1's? that doesn't make any sense .. since a Gorton 1 = a gorton D and we have gorton Ds on 1/8" all the time,
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
Comments
-
According to Balancing Steam Systems
A book I highly recommend just for the venting chart alone. The rest is a bonus. It is 1.2 cfm @ 1 o.z.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
thanks
I do have the book. unfortunately I didn't look thee1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
1/8"=gorton#2
1/8" pipe vents 1.2 cfm at 1 oz. Gorton#2 vents 1.1 cfm at 1 oz. I have put gorton#2 in 1/8" tapping with decent amount of success(3-4 min to end of main).0 -
that's what....
I ended up doing.. 1 piece of gorton# 2 on 1/8 th tap. I intend to install 2 pieces on each 6th floor convector in a building with other problems they are unable to address currently. the resident had more heat with a single # 2 when I left than when she woke up, and the whistling has subsided a great deal compared to the gorton 6 that was on.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements