Add A Rad
Chris M_2
Member Posts: 67
I have a 1 pipe steam system. I'd like to add a small radiator to an 8X12 room which is directly above
anoother room which has a radiator already. Can I simply remove the vent on the existing radiator (which is tapped
into a 1" endcap), and from that opening, add an elbow and riser to extend upthrough the ceiling and into the room to supply a new radiator?
Here's a crude picture of what I want to do:
IIIIIIIIIIIIII
Proposed Addition ---> IIIIIIIIIIIIII
IIIIIIIIIIIIII
i
i
i
i
i
i
i
IIIIIIIIIIIIII -i IIIIIIIIIIIIII
IIIIIIIIIIIIII
i
i
i
Riser to existing -> i
i /-Main Vent
---------------------------
anoother room which has a radiator already. Can I simply remove the vent on the existing radiator (which is tapped
into a 1" endcap), and from that opening, add an elbow and riser to extend upthrough the ceiling and into the room to supply a new radiator?
Here's a crude picture of what I want to do:
IIIIIIIIIIIIII
Proposed Addition ---> IIIIIIIIIIIIII
IIIIIIIIIIIIII
i
i
i
i
i
i
i
IIIIIIIIIIIIII -i IIIIIIIIIIIIII
IIIIIIIIIIIIII
i
i
i
Riser to existing -> i
i /-Main Vent
---------------------------
0
Comments
-
No.
But don't feel bad, most of my good ideas are illegal too. Maybe someone here can tell you how to do it right.0 -
i dunno know about legality of this...
but the condensate from the upper rad will sure have a hard time squeaking by the steam in a 1/8th hole.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
That won't work
for reasons already mentioned.
How big is the riser to this rad? Ditto the pipe from the steam main to the riser? How much EDR does the present rad have, and the one you're proposing?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Clarification?
I think he might have meant remove the cap and use the 1" tap, not the 1/8 vent hole. Even at that, still a bad idea and would cause more problems than solve. Don't do it like that, but post pictures of the existing rad and piping to it. There may still be another way.0 -
Yes.. Removing the Tap
Yes.. I meant remove the cap and tap into the existing rad where the vent is now tapped. But on 2nd thought, I think tapping into the BOTTOM of the existing rad (below the vent), adding an elbow and riser up to the new rad would make more sense. Here's a link to the rads I'm using. The existing one is a 72" X 24" , and the addition I'm adding will be a 24" X 24". http://www.steamradiators.com/pricing.html
No pics of my own at the moment.. I just re-visited this thread.
Thanks,0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements