Phase 3 rated for steam ?
Ron Jr._3
Member Posts: 605
Have a job where a Phase 3 ( installed by others ) is connected to a steam boiler ( installed by us in 2004 ) , and is heating up 2 zones of radiant and a zone of baseboard . The boiler side of the indirect keeps getting airbound . No leaks that I could see ( isolated the tank and filled with street pressure water on the boiler side . Was wondering if this was the best choice for the application ( tank in tank design and alot of the tank is above the boiler water line .
Thanks in advance . Gonna post a pic of this setup in the ugly system competition .
Thanks in advance . Gonna post a pic of this setup in the ugly system competition .
0
Comments
-
Re: rating on Phase 3
Ron, I think those have a max rating of 210 which would be exceeded if connected to a steam boiler?? I would be a bit concerned about that. Tim0 -
does the
1. phase 3 have an automatic air vent?
2.how is the pipeing conected to the boiler (bypass, thermonoter,)?
3.do you have flow control checks on both S&R.0 -
sorry
the bad spelling.0 -
actually... It does.
there is an air vent on the top of those phase3 indirect. Should be closed. probably fix the issue.0 -
it can
still suck air even when closed. i would valve it off. also needs 2 flow checks to keep water up there. it also needs to be piped properly (with by pass) to stop water from flashing to steam.0 -
This is why
I use super stor tanks. You will need to add a manual valve and force the water to fill the boiler side. It will eventually get air bound again though. Pumping towards the tank will help. also I think with the pressure differential between the domestic side and boiler side exceeds the requirements of the manufacturer.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Thanks guys
There was a 1/2 drain threaded into the top of the tank . Gotta purge it there too because there's alot of air trapped at the top if you only purge the piping itself . There was a flow check on the supply pipe only . But the supply was piped into the Burnham V8 well below the normal water line ( theres a dedicated tapping for an indirect or zone of heat ) . The return into the front lower left tapping . Piped Superstor Contenders the exact same way in the past with zero problems . They are coil indirects though ...0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements