Gas boiler still blowing off!!!

We changed the fill valve, expansion tank,relief valve and it still blowing off every few days. Boiler pressure is set at 20lb and high limit is 180F.



Has anyone ever had this problem, By the way this work was done by a pro!!

Comments

  • Mike Kusiak_2
    Mike Kusiak_2 Member Posts: 604
    Tank capacity?

    Is the expansion tank big enough to accept the additional volume of water created by thermal expansion? Is this a new system and did it ever work properly?



    Otherwise you must have some sort of leak of feed or DHW into the system. Is the DHW also heated by the boiler? The pressure cannot continue increasing unless there is some source of additional water entering the system.
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,371
    Check the pressure

    in the expansion tank and make sure it is matched to the working pressure. Why are you at 20 pounds pressure rather than 12 - 15 pounds? If the 20 pounds is required make sure the tank is large enough as the higher pressure will require a larger expansion tank
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    I agree with Charlie

    Why is the pressure set at 20 psi ? How high up is the heat going from where the boiler is ?  If the PRV is set at 20 psi cold it'll be very close to 30 psi when hot , even with a properly sized expansion tank . If the boiler is rated for it and you really need the increased pressure , I'd bump up the relief valve capacity to a 40 psi safety .
  • tim smith
    tim smith Member Posts: 2,807
    Re: expansion tank

    What size expansion tank did you put on, I know it is probably the same size but we have run into problems with tanks being marginally sized and even though they worked for prior 5 yrs or so, the new tanks would do the same thing. If I think a #30 extrol may do it, I go to a #60. Real hassle as you have found to chase pressure increase probs. I have had expansion tanks work fine for 5 yrs + and even though bladder still sound, they start to not accept the same amount of expansion they have prior. The only way I have been able to explain it is that maybe the bladder is sticking to the inner wall of tank or maybe the bladder has stiffened. I do not know but have pulled my hair out a few times over the years. Good luck. Tim
  • will smith_4
    will smith_4 Member Posts: 259
    Pressure issue

    Are you using a diaphragm or steel tank? If it's an old system, could the piping leading to the tank be partially plugged up?
  • STEVE PAUL_3
    STEVE PAUL_3 Member Posts: 126
    DON'T INCREASE SAFETY VALVE BLOW OFF SETTING!!!

    With all due respect to Ron,

     I WOULD NOT, replace the pressure relief valve with one of a higher blow off setting. The 30 PSI blow off valve is a code requirement. Using a valve with a higher setting would negate any manufacturers warranty and would be dangerous. After reading all of the previous and valid suggestions the one that I would recommend is to look for an isolating valve between the expansion tank and the boiler, if there is one, make certain that it is wide open. Your present pressure regulating valve setting of 20 PSI seems to be a rather high setting. 20 PSI is more than  enough to fill and purge a system in a 4-5 story building. Your PRV setting usually should be approximately  the highest point of the system in feet, divided by 2.33 + an additional 2-3 PSI... 2-Stories = 20', divided by, 2.33 = 8.58 PSI, + 3 PSI = 8.61 PSI. The 12-PSI factory setting on the PRV is more than adequate
  • Slimpickins
    Slimpickins Member Posts: 348
    indirect tank?

    If you have an indirect water heater you may have a leak in the coil and the house side pressure is raising the pressure on the boiler side. Isolating the indirect tank will answer that question.
  • tim smith
    tim smith Member Posts: 2,807
    edited December 2010
    Steve, are you thinking I was talking about relief valves???

    Expansion tanks!
  • STEVE PAUL_3
    STEVE PAUL_3 Member Posts: 126
    edited December 2010
    "STILL BLOWING OFF"

    TIM:

    The original post stated that after the replacements were made, it was "STILL BLOWING OFF".

     After almost 50 years in this racket, I can not think of anything on a hot water boiler that will "BLOW OFF" other than the relief valve. If I am missing something, I can learn something. Please educate me.  Again, I would re-state,  don't tamper with the relief valve, stay with a 30 PSI rated valve.

     Please don't take this response as argumentative, I just would hate to see someone injured or worse. 