piping installation correct?

My plumber who installed my Burnham steam boiler I think did an incorrect job on the piping. Here is a picture. I hear a little bit of water hammering during start up always, could this be related?



<a href="http://img98.imageshack.us/img98/5346/img00059201012011821.jpg">http://img98.imageshack.us/img98/5346/img00059201012011821.jpg</a>

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    your correct..

    have him pipe it according to the manual.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Rod
    Rod Posts: 2,067
    Diagram

    Hi- Here's a diagram which shows why the riser pipes from the boiler to the header need to be first in the order of the piping attached to the header, sloping toward the equalizer.

    - Rod
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,373
    Swing joints also require

    get the installation manual and say I want this or better, unless you never really paid for a complete installation, was his bid quite lower than the rest? No talking of numbers please but this was the low bider right?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Oak Park Electric
    Oak Park Electric Member Posts: 54
    Metal octopus

    2"  cast elbows must have been on sale...



    The diagram Rod posted is right on,  that piping is wrong and it is why you are getting hammering at startup.  Hopefully the installer left the manual, if so look at the section on piping and see how it should look.  If not, post the model no.  of the boiler and someone here will have the correct piping diagram and recommended pipe sizes.  The header should be a larger size that the risers, and a drop header will give you dry steam and allow for pipe expansion without trying to push the boiler sections apart.  If this guy doesn't want to fix it, or has no idea what you are talking about, try to find a real steam pro to look at it.