shocking a concrete slab
Options
ecletrical
Member Posts: 22
I have Wirsboro hePex in this slab. What is the highest temperature that the slab can take (not the hePex Max temp) before thermal stress could cause damage to the slab? I guess it depends on the delta T between slab temperature and tubing temp. Any ideas about what is considered safe?.
0
Comments
-
480 three phase...
Oh, not THAT kind of shock eh :-)
With a conventional heating system with a capacity of less than 100 btu's / sq ft per hour, you will play hell thermally shocking a conventional concrete slab.
In my 35 years of travel, I have seen one slab thermally shocked, and it was a snowmelt system with a steam boiler that could dump 300 btu/sq ft/hr into the slab on a hospital ambulance approach ramp. The concrete spalled up around the supply lines.
Believe it or not, the Edison Institute had some designs a while back of electrified concrete. They were looking at the possibility of using this electrified concrete for snowmelt applications on bridges and highways. This was back about 5 years ago...
ME0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements