Honeywell aquastat setpoint temperature shift?
LarryC
Member Posts: 330
Greetings,
My hot water boiler uses a Honeywell triple aquastat L8124L. I was observing its operation last night and noticed that the setpoints idicated don't seem to agree with the existing temperature / pressure gauge.
I heard the safety valve vent. I had previously added some water so I wasn't too concerned about the valve lifting. When I went down to investigate, the temp / press gauge was reading about 210 F and about 10 psi. I noticed one air vent was making noise like it was releasing air. The high limit was set to 180 F, differential to 20 F and the tankless limit was set to 140 F. I turned off power to the burner and let the thermostat call for heat cool down the boiler to about 180 F.
Because the pressure / temp gauge was reading around 210 F and the air vent was releasing gas, I believe the gauge is accurate. <strong>VALID ASSUMPTION ???</strong>
Assuming the gauge is correct, I set the high limit to 170 F. and turned the burner back on. Watching the boiler thru a couple of cycles and the burner turn off point is about 185 F and the turn on point is 170 F. As I understand the operation of the L8124L, the burner should turn off at 170 F and turn on at 170 -20 = 150 F during a call for heat. <strong>IS THIS STATEMENT CORRECT ??</strong>
What could cause this behavior?
Thanks for your help.
I would
Check the control sensing bulb to make sure it is bottoming out in control well. The more they are out of the well, the less accurate they are0