Main vents
acl10
Member Posts: 349
My system does not have any main vents. It does not look like there ever were any because the mains have no place to put one. Is this the way it should be? It was installed like that when the house was built about 80 years ago.I installed Gorton D on most of the radiators.
0
Comments
-
Some systems were built that way
but they should have main vents added. This will make them heat faster and more evenly. How long are your steam mains and what pipe size are they?
Also, large rad vents like Gorton D or Heat-Timer Vari-Valve units can vent too fast for the condensate to return in the runout, which can cause banging. With proper main vents you don't need large rad vents.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
How do you add main vents
How do you add main vents? There is no place to screw them in. The main pipe is 2 inches I think0 -
Drill and tap
You could drill and tap into the main to mount a vent and that could be tough if your too close to the ceiling, the hole has to be at the top of the pipe. If you do drill and tap start small and go up in drill size incrementally til you get the right size hole. that way you will end up with a round hole
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
alternative main vent location
remember the vertical pipe coming down in the dry return could also be a location for the main vent antler. naturally, it should be as high as possible so as to keep its feet dry.--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements