Dual Temp Hydronic System
John West
Member Posts: 3
11-30-2010
System:
1 Story Hydronic Dual Temp System
1 Chiller--1964 Worthington
1 Boiler-1964
1 Dual Temp Pump
1 Expansion Tank
1 Diverting Valve-to distribute Water flow through Boiler or Chiller.
1 Mixing Valve for Hot Water Reset on Outside Air
1 Safety-Chiller--Must be below 90 Degrees on Loop to Run
1 Safety-Boiler--Must be above 65 Degrees to have Boiler Run
1 Changeover SWitch--Changes at 58 Degrees--Above -Cooling-Below-Heat.
Questions:
1. What is the Proper way to Drain and Refill a Expansion Tank--I have always been taught to Valve Expansion Tank off fvrom System--Run a Hose to a Drain--Loosen the bottom of the Airtrol and allow all Water to Drain out--Close Drain--Open Tank to system--Keep Airtrol Loose until you see Water come out then Tighten and allow to complete Fill--Should be Air Gap in Sightglass when Finished.
Question 2:
If Dual Temp System has been Over Pressurized by a Defective PRV-Would you Bleed the Air from the Top of the Expansion Tank to Lower Pressure--Would this let your Air Pocket Out??
Would it be ok to raise the RElief Arm to get Pressure to Normal after installing new PRV--any more Ideas??
Question #3:
When dealing with a Dual Temp system--Should the Boiler-Water Pressure be the same as the Dual Temp Pump Pressure--in Heat-We are varying about 6 PSIG between the Pump Pressures and the Boiler Pressure??
The Expansion Tank we have is:
S/N-21791
Dia-24
Length-78
125 PSI at 650 Degrees
Stonesteel Brand
Airtrol--ATF-12
System:
1 Boiler-1964
1 Dual Temp Pump
1 Expansion Tank
Questions:
Question 2:
Question #3:
S/N-21791
Dia-24
Length-78
Stonesteel Brand
Airtrol--ATF-12
- 120 Geothermal
- 169 Indoor-Air Quality