CFM = vent size?

jp741
Member Posts: 31
I was wondering when a manufacturer of a main vent for a single line steam system refers to vent size is that the same as cfm? For example groton #1 has a cfm of .33 maidomist refers to a .1825 vent size, are we comparing the same thing?
0
Comments
-
hmm .. maybe
maybe maybe, Maid-O-Mist is listing the orifice diameter (0.1825 inches??) whereas the CFM figure from the Gorton #1 is a rate of flow (0.33cubic feet of air will pass through per minute).1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0