too much water

I HAVE A NEWW BURNHAM K 5007 BOILER THAT WHEN IT BUILDS STEAM IT ADDS WATER, I SKIMMED BOILER 4 TIMES AND DRAINED AND PUT 3 CAN OF SURGEMASTER IN IT. I HAVE A 4IN SUPPLY AND A 2IN WET RETURN THE WATER GOES UP A INCH IN THE GLASS EVERY 24 HOURS WHY CANT I FIND A HAPPY MEDIUM ON THIS JOB IT HAS BEEN RUUING FOR 2 MONTHS. PLEASE HELP, IT HAS A NEW M&M 247 FEEDERON IT 

Comments

  • jpf321
    jpf321 Member Posts: 1,568
    clean your return

    this seems to be an ongoing theme this year .. you likely have a very slow return, either replace it or clean it thoroughly. this is evidenced by your auto-feeder kicking in .. and your water level RISING .. if the auto-feed was kicking in and the water level was staying steady, then you would be looking for a leak. in this case, the auto feeder adds water, but it eventually all comes back .. hence rises. 
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • sight-glass too full?

    try to get every bit of the surgemaster out by draining, and  skimming etc. when you have pure water only in the boiler, you can evaluate the problem more accurately also, turn off any auto-feeder you may have, so you can see the real waterline fluctuations.--nbc
  • moneypitfeeder
    moneypitfeeder Member Posts: 252
    leaky valve?

    Don't know If this correlates, but last year after we bought our house when we fired up our boiler the shut-off valve to the manual feed line was leaking, so although the autofeed wasn't supplying the water unless called for, the boiler was being filled from the manual side, and the pressures were all set wrong, our steam boiler ended up pushing water 3 stories up and filled all the rads! It took forever to drain all that out..hope you find your answer and good luck!

    Dee