Relationship between amount of water and pressure
wiley
Member Posts: 16
Hi All-
First time steam owner here - with a 1940 crane boiler which has been working very well. Looks like it was converted to an oil burner at some point.
My question- Since having the boiler the pressure has been running a bit high - 3psi
The water in the sight glass was about 1/3 of the way up the column, which the plumber felt was good.
Recently I drained the boiler, refilled, and now the water in the sight glass is at the 1/2 way point. Pressure in the system is at a steady 2psi
Is there a connection between more water in the system and the pressure being created?
Water and pressure
The amount of water ion a steam boiler should not make any real difference. Does the boiler cycle off on high limit or just when the thermostat is satisfied?
0-30PSI gauges are not very good down at the low end, what are the settings on your Pressuretrol? Does the gauge read zero when the boiler is cold or just warm? Usually setting the tab in front to 0.5 and the white wheel, under the cover, to 1 is about as good as you get get with a Pressuretrol. For lower pressure you would have to use a vaporstat. With a vaporstat you usually want to add an Auxiliary low pressure gauge 90-3PSI or even a 0-20OZ).
3PSI gauge0 -
Water/steam pressure
Thanks for your response Bob - It appears that my boiler is cycling off at the high limit, not when the thermostat is satisfied.
Will check the setting on the pressuretrol - not sure of the current settings.0
- 114 Geothermal
