Is pex safe
leaking
Member Posts: 63
Is pex safe to use for piping to radiators on boilers that can reach 200f. What if the aquastat fails and temps go higher. Is it even logical to consider Pex for high temp boilers where pressure may be 20 to near 25lb. It sounds risky and unsafe.
0
Comments
-
pex
Pex is rated 100 lbs at 180 degrees for domestic hot water0 -
PEX Safety
To answer your question, no, PEX is not safe to use in any kind of heating system unless you install your own safety high limit. Ever since I had a runaway boiler that melted the PEX tubing supplying radiators, I've installed a high-limit aquastat on the supply piping.
If you are uncomfortable even with the use of your own high limit, use copper.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
yes
it is safe.
Is there something more behind this question?0 -
why the heck
would you allow your boiler to run to 200 deg F in this day and age???Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
Solid fuel boiler
Most of the barrier pex I have seen lists a rating of 80 psi at 200 degrees F. Look up the specs on your tubing to be sure.
NRT_Rob, 200F is not uncommon with wood or coal fired boilers in the spring and fall. e.g. I have a dump zone set at 200F on my coal boiler.
-Rob0 -
so add
a tempering valve...Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements