Buderus G125BE Update 2 Yrs 1065 Hrs
carl_nh
Member Posts: 27
I wanted to thank you all for your feedback and that we are very pleased with the performance and economy.
Well, thought to give a short update on the Buderus G125BE selection and overall performance.
Installation Feb 2009 G125BE 21 72K BTU w/LT160 Horz Tank, 3 Grundfos Circ Zones, Taco Zone Control, 1 Grundfos HW loop, Ultra Filter
Feb 2009 to Feb 2010 used 450 Gal Oil - vs 890 and 900 gal two previous seasons. Just installed a new Roth tank with Rollie Heater to replace inside horizontal tank in crawl space.
Tracking usage it is burning .64 GPH @ 280 PSI setting
Nov. 2010 Total Hrs 1065 Still Burning Blue Flame Changed Ultra Filter one Time
Vacuum/Cleaned Unit 3-4 times over last 2 yrs - still working fine
Most Recent Readings: C75 Comb Analyzer - Original Nozzle and Settings of Air @ 4.5 and Pump Pressure @ 280PSI
Outside Air Temp 48*
Boiler Temp 140
O2% 3.2
CO2 13.3
CO PPM 37
COaf 43
Flue temp 265
Efficiency 89.6
Loss 10.4
Excess Air 18.0
The boiler tech and I took readings over 90% Eff @ 125* and lowest was 89.2 Eff at 165*. Also CO2 was in Buderus spec range at 13.3 in all cases.
What was interesting is these # are better than when brand new! We decided not to change anything at this time.
What are you guys seeing with these units as far as perfomance?
Are we in good shape with these specs after over 1000 hrs operation?
Thanks
Well, thought to give a short update on the Buderus G125BE selection and overall performance.
Installation Feb 2009 G125BE 21 72K BTU w/LT160 Horz Tank, 3 Grundfos Circ Zones, Taco Zone Control, 1 Grundfos HW loop, Ultra Filter
Feb 2009 to Feb 2010 used 450 Gal Oil - vs 890 and 900 gal two previous seasons. Just installed a new Roth tank with Rollie Heater to replace inside horizontal tank in crawl space.
Tracking usage it is burning .64 GPH @ 280 PSI setting
Nov. 2010 Total Hrs 1065 Still Burning Blue Flame Changed Ultra Filter one Time
Vacuum/Cleaned Unit 3-4 times over last 2 yrs - still working fine
Most Recent Readings: C75 Comb Analyzer - Original Nozzle and Settings of Air @ 4.5 and Pump Pressure @ 280PSI
Outside Air Temp 48*
Boiler Temp 140
O2% 3.2
CO2 13.3
CO PPM 37
COaf 43
Flue temp 265
Efficiency 89.6
Loss 10.4
Excess Air 18.0
The boiler tech and I took readings over 90% Eff @ 125* and lowest was 89.2 Eff at 165*. Also CO2 was in Buderus spec range at 13.3 in all cases.
What was interesting is these # are better than when brand new! We decided not to change anything at this time.
What are you guys seeing with these units as far as perfomance?
Are we in good shape with these specs after over 1000 hrs operation?
Thanks
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements