radiators vents get water in them

JIM W.
JIM W. Member Posts: 16
WE HAVE USED DIFFERENT STYLE VENTS, THE LAST WERE HOFFMAN1A STYLE.  THE VENTS GET WATER IN THEM AND STOP VENTING.THE CUSTOMER REMOVES VENT, DRAINS WATER FROM THEM PUTS BACK ON AND THEN THEY GET HEAT.  THIS IS THE MOST COMMON ON 2ND FLOOR RADIATORS, BUT HAS HAPPENED ON OTHERS FROM TIME TO TIME.  WE INSTALLED A VAPOR STAT FOR CONTROLLING THE PRESSURE AND HAVE IT SHUTTING OFF NO HIGHER THAN 1.5 PSIG.  

WHERE SHOULD WE BE FOCUSING OUR EFFORTS?

Comments

  • BobC
    BobC Member Posts: 5,495
    Water in a steam radiator

    I assume this is single pipe steam.



    Make sure all the piping and radiators allow the condensate to return to the boiler, don't depend on your eyes - use a level. Make sure all the radiator input valves are fully open, partially closed valves trap water in the radiator.



    Is there any banging going on and if so, when? At the start, middle or end of the heating cycle? What is the near boiler piing like, is it per the manufactures spec?



    Post some pics of the boiler, the near boiler piping, and one of the problem radiators 9include the valve and vent).



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Dave in QCA
    Dave in QCA Member Posts: 1,788
    strange problem!

    Here is a link to the Hoffman Specialty website that has a picture of the 1A vent.   http://www.hoffmanspecialty.com/pdf/hs900/HS900-1A4070A.pdf

    The little tongue part that protrudes from the threads is intended to channel any water that naturally forms as a result of condensation, back out of the vent and into the radiator.  In order for this to work, it must extend past any surrounding material.  So, if this vent is installed in a coupling on the end of a pipe nipple, it will not drain.   It must be threaded directly into the cast iron radiator threads.

    Can you provide a picture of a typical installation?

    I had a radiator in a building I bought, that someone had installed a Hoffman model 41.  That is a vent that has the threaded nipple on the bottom.  They had it installed into a common radiator, so it was laying sideways.  Of course, it didn't work so well!

    Again, more information and pics would help a lot.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • JIM W.
    JIM W. Member Posts: 16
    Thanks for your response,

    Yes it has the tounge and is directly into the radiator.  When

    We installed the 1A vents I thought this feature would help with the issue.

    Previous vents were a style that did not have this.
  • Patrick_North
    Patrick_North Member Posts: 249
    Same problem...

    I had the same problem with the 1A's in a big way before we replaced our boiler. A new boiler - and with it much drier steam- greatly remedied the problem, but not entirely. On the radiators where this was most troublesome I've replaced the Hoffmans with Gortons- problem solved.

    You could repipe your header to help dry out the steam, but I'm guessing that's a bridge too far. Despite it's design "features," it's my experience that the Hoffman 1A just does not handle water very well.

    Good luck,

    Patrick
  • FJL
    FJL Member Posts: 354
    Water In Vent

    I have had this problem in my apartment.  New boiler was installed in 2008.  Gorton valves on all radiators.  Some vents have a moist hiss.  One radiator, connected to the riser farthest from the boiler, about 55 feet away, has the most moisture.  It doesn't spit water, but water will collect on the top of the Gorton vent, right outside the hole.  I'd like for it to be dry but no water is spitting out and onto the floor, so I just live with it.  The rads are properly tilted back toward the valve, the valves are all open, and I've even shimmed the rads so they don't tilt one way or another.  I can't think of anything else to do.
This discussion has been closed.