Riello Lesson Learned
Coany
Member Posts: 90
in Oil Heating
A few days ago I got a no heat call on a nearly new boiler with a Riello Burner.
The installers had not changed the oil line or filter and the oil system was plugged.
So I changed the b4 and the ssc126G strainer and primed it up.
It just ran and ran, in pre-purge, would not signal the oil valve,and didn't lock out either.
I went though everything twice and was very frustrated .
I'll come back tomorrow and tell you the embarrassingly simple answer
any guesses?
any guesses?
stuck closed oil valve?
are you sure you have them all opened?Cost is what you spend , value is what you get.
cell # 413-841-6726
was it
running but not firing when you got there, or did you have to reset it? Could be a few things goin on here. What control is on it? I haven't seen the latest Riello control, but maybe they have a priming mode like Honeywell/Beckett controls do that will run like 4 minutes without locking out. Curious here. I don't thing you are back feeding. I'd also check control mount plate for bent pins, crossed connections, etc0 -
Re:Riello Lesson Learned
The attached file should help.There was an error rendering this rich post.
The answer
I moved my drop light a bit further away.
It was seeing some stray light, which prevented it from coming out of pre-purge.
I had hung my drop light about two feet directly above the blast tube.
I won't do that again.There was an error rendering this rich post.
Riello purging tip
I install Riello burners almost exclusively. And service even more of them.
Here is an oil purging tip. Take the primary off. leave the drawer assembly cover in place. Place your jumper clips on terminals 5 & 6 for the primary. Turn on the service switch. The motor will run and the oil valve will open, but it cannot fire. You also don't have to fuss with the safety timing. When you are done, close the bleeder, pull the jumpers and put the transformer back on and fire it.
I do this 3 or 4 times a day sometimes and it never fails.
Good luck.0 -
Another tip
Leave the primary in . Let the burner run . Right when you hear the " click " of the igniter , hit the reset button . It'll cycle again without waiting for the reset timeout . Good for priming if you think it'll only need 3 or 4 resets .0