BTU meters

NRT_Rob
NRT_Rob Member Posts: 1,013
what's anyone using out there for hydronic BTU metering? the Istec meters look nice, but is anyone using them?
Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.

Comments

  • hot_rod
    hot_rod Member Posts: 23,191
    How accurately?

    Many of the solar controllers read the delta T then you input a flow rate to get a fairly close BTU calculation.



    Next step would be the Grundfos flow sensors measuring flow and temperature. There seems to be some question regarding their accuracy with glycols as the fluid changes so much across temperature ranges.



    Then the pulse sign rotary meters..



    Most of the new solar controllers, and energy meters will accept input form any three of these choices. The large pipe sized water meters get fairly $$.



    Beware many of these meters read out in metric units only, possibly the brand you mentioned?



    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream