Can An Old Return Line Cause Wet Steam ?
SteamHeat
Member Posts: 159
If your condensate return line is old and has a nice inner liner of bioslime / crud effectively narrowing the inner diameter of the pipe, could this cause your steam to be wet ?
0
Comments
-
it's possible that ..
slow returns *MAY* be causing the water to stack up above your "A" Dimension and spilling out into your overhead mains, this would cause wet steam for sure. Don't forget that if you have 2" mains, and you are 2" above your "A" Dimension, your mains (at least the ends of them) are FULL UP with water.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Good Points.
Thank you. These are very good points to consider.
I am going to be replacing my return line soon and I was wondering if it might solve a gurgling radiator vent valve that does not seem to have any other explanation.
Regards.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements