Riello Burner not firing...
jpf321
Member Posts: 1,568
Riello 40-F5, brand new .. When I flip on the power, the electronic shutter opens, the blower blows, in a few secs I hear what sounds like a pipe with running domestic pressure water (a hiss like sound) then lockout.
I have a tiger loop (2-pipe) and see that there is fuel in the dome. All connections are tight.
When I shine light in air tube cover, as per 2-pipe pre-purge directions, no hiss and no lockout.
I have left it pre-purge (using the light) for several minutes, is there an average pre-purge duration?
When I open the bleed valve while blower is on, fuel comes shooting out.
I don't hear any "clicks" per se, could it be a solenoid?
I must admit, that when I first wired it, I connected the Aquastat to 7
& 8 rather than 1 & 2...(the little circuit diagram card that is
inserted in the primary has them labeled backwards. Only the stampings
on the plastic are correct. Why they enclose that card, I have no idea.) EvenI had them backwards, I did get fire for a couple of minutes. It went off when I shut off the switch and has never come back.
Could I have damaged the pump?
Since the blower blows, the motor is OK correct?
Could it be the 12.5uF Capacitor? I hope so. I have a local shop that carries Riello parts open today, I'm open to suggestions.
Does someone have the Riello Troubleshooting table that they'd like to reference/share?
FYI, Riello Manual is here: <a href="http://is.gd/gtR5v">http://is.gd/gtR5v</a>
I have a tiger loop (2-pipe) and see that there is fuel in the dome. All connections are tight.
When I shine light in air tube cover, as per 2-pipe pre-purge directions, no hiss and no lockout.
I have left it pre-purge (using the light) for several minutes, is there an average pre-purge duration?
When I open the bleed valve while blower is on, fuel comes shooting out.
I don't hear any "clicks" per se, could it be a solenoid?
I must admit, that when I first wired it, I connected the Aquastat to 7
& 8 rather than 1 & 2...(the little circuit diagram card that is
inserted in the primary has them labeled backwards. Only the stampings
on the plastic are correct. Why they enclose that card, I have no idea.) EvenI had them backwards, I did get fire for a couple of minutes. It went off when I shut off the switch and has never come back.
Could I have damaged the pump?
Since the blower blows, the motor is OK correct?
Could it be the 12.5uF Capacitor? I hope so. I have a local shop that carries Riello parts open today, I'm open to suggestions.
Does someone have the Riello Troubleshooting table that they'd like to reference/share?
FYI, Riello Manual is here: <a href="http://is.gd/gtR5v">http://is.gd/gtR5v</a>
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
Comments
-
TS chart
Will this attachment help?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
fantastic Bob...but ...
after 2hrs sleep, I was up bright and early with a clear head .. and realized that I had probably burnt out the valve coil .. a couple bucks later, I had one in hand, installed it and now she fires up perfectly.
if you ever put your aquastat on 7 & 8 ... you will burn out your coil :-)
in business, and my wife is eagerly awaiting the results ...1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Glad to hear it's working
I have done silimilar in the past. The worst is realizing it's your own fault but you had some "help" from that botched instruction sheet. The best news is that is one mistake you won't make again!
I would send Reilio a note thanking them for their help.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements