Prestige Solo 110 with reverse indirect
Gordan
Member Posts: 891
Shooting for simplicity and efficiency. The below diagram is my best shot so far at providing adequate isolation, purging and draining ability for the boiler, the tank and the system with a minimum of fittings. How'd I do?
0
Comments
-
One concern I have with the PS110...
...is the built-in circulator with a check valve in a downward-facing orientation. Theoretically, regardless of the other piping details, this would be a candidate spot for air pockets to form. Is this not a concern in practice? I'd imagine not, considering the number of PS110s installed...
I need some kind of air vent between the tank and the boiler, but I'm wondering what would be a good enough way and place to install it, given that I don't want to repipe the boiler internals.0 -
PS110
The PS110 Prestige Solo comes with a Grundfos UPS1558 but it does not have the check valve in it.0 -
And even if it did...
...it would be an easy task to remove it. Thanks! Does the rest of the piping diagram seem sane? For a single-zone load, the manual shows the air eliminator/tank/fill on the return, but that seems like it would not give the air eliminator the best shot at doing its job.0 -
Duplicate
Duplicate.0 -
-
Using an Alpha for the system.
I'll be wiring the internal pump to the DHW terminals. I'm not piping the boiler primary/secondary, but pumping system flow right through the boiler.
Based on the illustrations in the manual, the two supply outlets would seem to be equivalent in every way. Is that another wrong assumption on my part?0 -
Good Question
I don't know.0 -
I cannot help but ask
Where is the condensate drain dumping?0 -
Sorry, didn't include that on the diagram...
Busy enough the way it is. :-) Neutralizer, then drain.0 -
A different way...
This would be more in line with what their manual suggests. I've relocated the air eliminator, feed and expansion tank to the return side, and removed some check valves which I thought were not necessary. There's a heat trap on the supply side of the reverse indirect. Both the system and the reverse indirect would be plumbed in 3/4" PEX-AL-PEX (aiming for low flow rates and wide delta-T on the DHW side; the space heating side should top out at 4 GPM.)0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements