Black water in sight gage
Joe V_2
Member Posts: 234
Boiler, Burnham IN5
Second heating season.
Drained boiler(water was clear, mild rust color) to pull LWCO probe and refilled, adding a 1/2 bottle of squick, fired, and blew down to test LWCO. Refilled and water came up pitch black.
Water line is stable and the system is quiet. Should I skim again? Flush? Last heating seaon the water was clear after skimming.
Second heating season.
Drained boiler(water was clear, mild rust color) to pull LWCO probe and refilled, adding a 1/2 bottle of squick, fired, and blew down to test LWCO. Refilled and water came up pitch black.
Water line is stable and the system is quiet. Should I skim again? Flush? Last heating seaon the water was clear after skimming.
0
Comments
-
squick = no substitute for skimming
i would drain, refill and boil to get the boiler full of pure water. squick will collect on the bottom, and in the LWCO, and form hard deposits, and probably serves no purpose except the enrichment of the manufacturer.--nbc0 -
Realy?
I thought the idea was to scavenge oxygen to reduce rest and sink particulates to bottom of boiler. I wasn't trying to use it in place of skimming...That was done on start up last year.
So, squick is a bad idea?0 -
Boiler Water
Hi Joe-
Whether or not one uses boiler additives seems to be a controversial subject among the pros. Some are in favor of them and others are not. I have a tendency to think a lot of this decision is driven by "how quick can we get the waterline settled down and get on to the next job" rather than by what is necessarily good for the boiler in the long run. The pro is stuck in a bit of a hard spot here. If additive has the advantage of cutting time (and saving the customer money) is he obliged to use it?
It also depends on what type of boiler you are using them on. Burnham uses push nipples between the boiler sections where other manufacturers use a seal. If your boiler is the seal type you want to make very sure that the additive you are planning on using doesn't affect the seals between the sections.
From what I've read I tend to go with the no additive crowd though it fact I'm really a "fence sitter" as I've been using Rhomar Products in my boiler http://www.rhomarwater.com/products/residential-steam-system/ when I have it shut down during the summer and for cleaning but use plain water during the heating season. I would just keep flushing your boiler until it ran clear. As for the dissolved oxygen, just make sure you bring your "new" water to a boil as this drives off any excess oxygen.
- Rod0 -
Thanks Rod
I did not know the use of additives like squick was controversial. On the other hand, it seems to have found a mother load of oil that I was unaware of which I will flush out tonite.
Joe0 -
Black water
...was just that. It wasn't oil at all. The water was the same that comes out of a fire sprinkler system- black and smelly-biological corrosion in black pipe. Likely created by puddles in the return piping over the summer brought to the boiler by running it in preparation for this winter.
It took an hour of flushing before the water ran clear. I doubt, at this point, that squick was any help.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements