Just added to the Library
DanHolohan
DanHolohan Member, Moderator, Administrator Posts: 16,686
One of the earliest editions of what became Consumer Reports. This issue covers Heating and Ventilating, Lighting, Fire Extinguishers, and Building Materials. Enjoy!
<a href="http://www.heatinghelp.com/article/133/For-the-Homeowner-Builder/1812/Consumers-Research-1931">http://www.heatinghelp.com/article/133/For-the-Homeowner-Builder/1812/Consumers-Research-1931</a>
Retired and loving it.
  • Brad White
    Brad White Member Posts: 2,399
    Remarkable...
    Worth reading, the treatise on coal, how even then, in 1931, they were critical of one-pipe steam, declaring it all but obsolete. The articles cited re: carbon monoxide, from 1923 no less, tells you that the past is prologue, once again. Good find, Dan!
    -Ernie White, my Dad
  • DanHolohan
    Glad you enjoyed it.
    You can see the roots of the magazine to come in this issue. Unbiased and blunt.
  • Rod
    Rod Posts: 2,067
    Great Reading!
    Thanks, Dan ! Great reading!
     Don't be surprised if it takes a bit longer than usual for the PDF to load.  Found an interesting statement on Page 8 - they use a factor of 150 BTU per square foot, per hour (no temperature stated) for HW radiator radiation. The "modern" factor is 180 BTU @ 190 F.    I wonder if this was a writing/printing mistake or "old think" and if "old think", why the change to the "modern" factor?
    - Rod
  • DanHolohan
    Rod,
    The 150 Btu/EDR would be from an average water temperature of 170 F.
  • Rod
    Rod Posts: 2,067
    "Standard"?
    Thanks Dan. I was just wondering if 150BTU (@170F) was the conversion "standard" at that time. I'm assuming that since they didn't have modulating that they thought in an "on and off" way.   The article does list 240 BTU s for steam. But steam is steam so you really can't use any other number.
     Have you had run across this 150 BTU "standard" in any of your other old books from this time period or before?  All others I have read use the 180 BTU (@190F) conversion factor.
    - Rod
  • DanHolohan
    Yes,
    150 Btu/Sq. Ft. EDR has been standard for systems that have water leaving the boiler at 180 and returning at 160. The numbers work like this:
    Average Water Temp.     Output in Btuh per Sq. Ft. EDR
    150                                           110
    155                                           120
    160                                           130
    165                                           140
    170                                           150
    175                                           160
    180                                           170
    185                                           180
    190                                           190
    195                                           200
    200                                           210
    205                                           220
    210                                           230
    215 (steam at 1 psi)                   240
    So when the average water temperature changes by five degrees F., the Btu output per sq. ft. EDR moves by 10 Btus.