Heat Dump ?
I have a job that will have 180 vacuum tubes tied into two 120 gallon dual coil tanks. An existing 120 gallon single coil tank will be at the end of the line and will be heated by a boiler when needed. This is a vacation home with four baths which should use more than the solar can put out when the owners are visiting. My problem is when they are not home for weeks at a time. They want to use the solar to do something usefull, not just dump it. No pool or hot tub, just radiant heat and snowmelt. The snowmelt will be a good dump for the summer months. I'm trying to keep this as simple as possible. Anyone have experience with a system like this? Thanks.
0
Comments
-
yes
it's called a drainback system
It sounds like you might end up spending more energy dollars to dump un-useable energy, then they actually harvest and consume, if the home is not occupied much.
Crunch some number with RET screen or one of the solar design programs using actual occupied days of DHW used.
Or solar powered AC units.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Options?
Thanks Hot Rod. Drainback is not an option because of location. The builder and owner both think after the tanks are satisfied it shouldn't be a problem to have the solar heat some of the house or melt a little snow. Easier said than done as I'm finding out.0 -
sounds like a lot of collector
check the manufacturers or SRCC data to see what sort of output you can expect from that size array. Then figure out where it will go all summer because it may cover the DHW load in just a few hours, IF they use some DHW. If not it may run to dump all day long on the days when the home is empty.
Here is a dump radiator that was installed on a large commercial system I visited. The cost of running the pump and two large fans bites into that "free energy" figure.
Also a dump formula that may help you, thanks to Siggy and Appropriate Designs
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A lighter shade of green
I will push for a smaller array. I've come to the conclusion that the mechanical room is too small and the system gets too complicated to try and move solar heat around the house if and when its needed. I do it at my own home, but that's different. Thanks HR for your thoughtful responses.0 -
ask a dumb Quest....
why wont drainback work? What is special about your project that it can't work?0 -
Structural issues...
you would have to go up to make it back down. A trap in the line.0 -
location?
you didn't mention where the system is located, and what sort of heating load is present.
if a drainback isn't possible, and the customer wants to do a large system, you could use the system to dump heat into the snowmelt loops (assuming they're big enough), but that will use power.
if you want a dedicated dump that will not use much more power than the original system, use a diverting zone valve on the supply to the panels that diverts solar fluid to a set of fin tube elements. based on advice from older installers, I've used 1 foot of E-75 (3/4") element per 4 square feet of net apature of collector and had an unloaded temperature of 160 on the hot side, a 5 degree drop thru the 200 feet of piping to the house and whatnot, and then 15 degree drop thru the fin tube element.
I've also just pumped the supply to the collectors to a caleffi high flow TMV, which diverts anything over 150F to a dump loop designed similarly. works great with no additional power usage. just use a valve with a high CV and you'll be fine.0 -
Steamback
See the Steamback Design thread to understand how you can reject the heat before it is collected.There was an error rendering this rich post.
0 -
Vacation Homes
Putting solar on a rarely used vacation home is a bad use of resources, and no one has yet been successful with seasonal thermal storage.
Grid-tied PV IS good at seasonal storage, however, and would therefore be a much better investment.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements