piping suggestions

IZZY
IZZY Member Posts: 59
Need suggestions for extending heating system into an addition. I've included a sketch to try to clarify.  Hope it opens properly.

The system is a single zone hot water monoflo system.  The house is 2 stories, plus basement, with attached garage.  Basement mostly below grade, addition to be built above garage.  Sketch shows the monoflo loop, and I drew 1 radiator on 1st and 1 on 2nd floors to illustrate typical piping of system.  Incidentally, all tees are 1" x 1/2".

Plan is to add sunrads in addition in order to match rest of existing house.  New piping has to run from basement to 2nd floor, and then to new rads, and that's a pretty long run for a monoflo tee (huge pressure drop I think).

I want to keep the new rads on the same zone, and I'm shooting for simplicity.

Any ideas would be appreciated.  Thanks.

Comments

  • JStar
    JStar Member Posts: 2,752
    I would...

    ...use standard tees, and set up a secondary loop with it's own circulator.
  • Gordan
    Gordan Member Posts: 891
    Is that diagram correct?

    It shows TWO monoflo circuits piped in parallel. If that's correct, then adding more diverter tees, or anything else that adds appreciable pressure drop, to one side could affect the flow on that branch, unless you have a way to rebalance. Running the new circuit off of a pair of closely spaced tees with their own circulator, as JStar suggests, would seem like the least treacherous path; then the only thing you've got to worry about is temperature drop in the main. Since all other radiators are already sized the way they are sized, you might be best off teeing in AFTER all the other emitters on the branch, and sizing the radiators in the addition for whatever supply temperature will be available at that point.
  • IZZY
    IZZY Member Posts: 59
    wiring?

    How do I control the circ?  Do I wire it in parallel with the main circ?
  • IZZY
    IZZY Member Posts: 59
    pipng

    The system is in fact piped this way, although there are many take-offs on the loop.  Each radiator has a standard tee on the supply side and a monoflo tee on the return side.  I'm not that farmiliar with monoflo systems, but I thought that this was the way it is supposed to be done.  I can say that the system works fine and the rads at the ends of the 2 split loops are about the same temp (to the touch).  If it can be refined, I'm open to ideas.  Thanks.
  • Gordan
    Gordan Member Posts: 891
    Now I'm even more confused...

    When you say "supply side" and "return side", do you mean relative to the radiator, or relative to the boiler?



    In a diverter tee circuit, also called one-pipe hot water, radiator risers are piped in series to each other to a common main that goes from boiler supply to boiler return - supply 1, return 1, supply 2, return 2, etc. Occasionally you could see an arrangement like supply1, supply 2, return 1, return 2 - this is to create a higher drop along the main between supply 2 and return 2, and force more flow into that branch, if necessary (typically only used for radiation below the main.)



    Is that how yours is piped - two of these circuits in parallel?
  • IZZY
    IZZY Member Posts: 59
    piping

    Yes, the pipe leaves the boiler, loops around the basement ceiling and returns to the boiler.  Along the way, there will be a standard tee, whose branch supplies a radiator (supply 1) and whose run continues on into a diverter tee, whose branch recieves the return from that radiator (return 1), then on to the next standard tee to supply the next radiator (supply 2), and the into the next diverter tee to recieve the return from the next radiator (return 2), and so on until the main loop returns to the boiler.  The only difference from this is that there are parts of the house where the rad on the 2nd floor (rad 1) is directly above the rad on the 1st floor (rad 2).  Here, the piping along the main is supply 1, supply 2, return 2, return 1. 
  • Gordan
    Gordan Member Posts: 891
    Ok, all's right with the world

    That radiators at the ends of both runs feel equally warm means that the two circuits are probably balanced well enough. Don't do anything to imbalance them. The closely spaced tees/separate circulator at the return end of one of the branches would be least likely to cause problems with existing stuff.
  • IZZY
    IZZY Member Posts: 59
    thanks

    Thanks a lot.
  • JStar
    JStar Member Posts: 2,752
    edited September 2010
    Wiring.

    You can wire a switching relay to a new thermostat in the addition to control the pump. Might as well set it up on its own zone while you're doing the work, and have the open framing. If not, you should have a dedicated switching relay for it anyway. You can use the dry contacts on the new relay to turn the boiler on at T+T. Or use the dry contacts on the aquastat to turn the secondary relay on.
  • IZZY
    IZZY Member Posts: 59
    wiring

    Thanks for the help.
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    How's he going to keep from overheating the rest of the house???

    If the addition is a higher loss appendage, it will probably call more than the core of the existing house...



    ME

    There was an error rendering this rich post.

  • IZZY
    IZZY Member Posts: 59
    good point

    I'm assuming the addition will have less of a heat loss due to the fact that the existing house is approx. 60 yrs old, where the addition will have the proper insulation, house wrap, etc.

    I was trying to keep the addition on the existing thermostat, but now that you brought that up, it might be better putting it on it's own zone.

    Incidentally, somebody suggested cutting in a tee after the circ pump on the supply side of the monoflo loop (at the boiler) and a tee at the return side of the loop (also at the boiler) to make it like a split zone.

    Any thoughts?
  • Gordan
    Gordan Member Posts: 891
    Right...

    I think a single zone approach, with the emitters in the addition being appropriately sized, would avoid those issues. The circulator for the addition runs when the system circulator runs. Simple control, enabled by appropriate design.