2-Pipe versus Primary/secondary
dba (aka damp head)
Member Posts: 3
In my quest to become acquainted with hydronic heating I've come across 2-pipe systems and primary/secondary arrangements
Could someone help guide me as to when one would be preferred over the other?
The primary/secondary seems "cleaner" for installation but each secondary loop requires its own circulator in addition to a more detailed calculation/understanding of the water temperature as it moves thru the primary loop. While the 2-pipe system is a little more straight forward and requires zone valves and/or balancing valves.
Thanks in advance for the help.
DBA (aka "damp head" ... but trying to get more "wet")
Could someone help guide me as to when one would be preferred over the other?
The primary/secondary seems "cleaner" for installation but each secondary loop requires its own circulator in addition to a more detailed calculation/understanding of the water temperature as it moves thru the primary loop. While the 2-pipe system is a little more straight forward and requires zone valves and/or balancing valves.
Thanks in advance for the help.
DBA (aka "damp head" ... but trying to get more "wet")
0
Comments
-
BIG Question
Damp Head, If you want to become a "wet head" I suggest you immerse your head in
a ........... couple of good books. The short answer to your question is " It Depends".
There are so many variables in architecture, heat emitters, heat sources, pumps, etc. that
there is no best. One fundamental design criteria that seems to be overlooked these days
is trying to keep the heat load and pressure drop as close to the same in each loop.
Good luck with your quest.There was an error rendering this rich post.
0 -
BIG Question
Double post, sorryThere was an error rendering this rich post.
0 -
Piping
I pipe primary/secondary (p/s) to keep the boiler happy. Let's say there are multiple zones and only one small zones calls for heat, the flow through that zone will not pull all the heat out of the boiler's heat exchanger, even if the boiler is modulating on low fire - the boiler will start to grumble. P/S piping always allows good flow through the boiler.
On the other hand, there are often older homes or apartments with one big zone where p/s piping would be a waste of time; pipe it 2-pipe since you get full flow on a call for heat.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Piping:
For what it is worth, I pipe all new and replacement boilers with a primary loop for the boiler and make secondary loops from the primary. That way, I know I will always have good flow through the boiler no matter what secondary zone is runing and it seems to solve all problems.
If it is a one zone replacement, I just use the closely spaced tee thing. If there is a indirect added, I use another set of closely spaced tees.
Never had a problem. If there were origonal design problems in the old system, they will not effect the qualities of the new boiler and piping.
Hydronics is very forgiving. You really need to work hard to screw it up. The fun is figuring out what is wrond and if it can be reasonably fixed.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements