Some formulas
Mark,
I couldn't find anything in the EDR book , I'll continue to look.
Ft./Lb.
Energy
1 HP 0.746 KW 746 Watts 2,545 BTU/h 1.0 kVA
1 KW 1,000 Watts 3,413 BTU/h 1.341 HP
1 Watt 3.413 BTU/h
1 Ton Ac 12,000 BTU/h Cooling 15,000 BTU/h Heat
Rejection
1 BTU/h 1 BTU per hour
1 BHP 34,500 BTU/h (33,472 BTU/h) 34.5 Lb.
Steam per hour 34.5 Lb. H2O/Hr. 0.069 GPM 4.14
GPH 140 EDR (Sq. Ft. of Equivalent Radiation)
1 Therm 100,000 BTU/h
1 MBH 1,000 BTU/h
1 Lb. Stm./Hr. 0.002 GPM
1 GPM 500 Lbs. Steam per hour
EDR Equivalent Direct Radiation
1 EDR 0.000496 GPM 0.25 Lbs. Steam
Condensate per hour
1000 EDR 0.496 GPM
1 EDR Hot Water 150 BTU/h
1 EDR Steam 240 BTU/h
1 EDR 240 BTU/h (Up to 1,000 Ft. Above Sea Level)
1 EDR 230 BTU/h (1,000 Ft–3,000 Ft. Above
Sea Level)
USEFUL HVAC CONVERSION MEASURES (cont.)
1 EDR 223 BTU/h (3,000 Ft.–5,000 Ft. Above Sea Level)
1 EDR 216 BTU/h (5,000 Ft.–7,000 Ft. Above Sea Level)
1 EDR 209 BTU/h (7,000 Ft.–10,000 Ft. Above Sea
Level)
Flow
1 mgd (million gal. per day) 1.547 Cu. Ft./Sec.
694.4 GPM
1 Cu.Ft/Min. 62.43 Lbs. H2O/Min. 448.8 Gal. per
hour
Metric Conversions
KJ/Hr BTU/h 1.055
CMM CFM 0.02832
LPM GPM 3.785
KJ/Lb. BTU/lb. 2.326
Meters Feet 0.3048
Sq. Meters Sq.0 -
Gpm=btu/500
Mark: if we Take GPM = BTU/HR
500 (water) X temp diff deg F
So if we take 150 as the average BTU /ft. EDR at 170 degree water say we have 17 ft EDR. 17X150= 2550/500= 5.1 gal It sounds like it might be close. That is the amount of water needed for that many BUT's. ?????0 -
Found it!
Mark:
Burnham's heating helper page 50. I tried to copy paste but the columns when all over.
I tried to doctor up the water content column.
MC
A. RADIATION
Based on Sq. Ft. Rating Water Content/Gal. Weight/Lbs.
Slenderized Radiators 0.066 4.5
Large Tube Radiators 0.103
Column Radiators 0.188
Convectors (Non-Ferrous) 0.004
Convectors (Cast Iron) 0.040
Radiant Radiators 0.066
Base-Ray (Cast Iron Baseboard) 0.066
0.066
0.103
0.188
0.004
0.040
0.066
0.066
4.5
5.25
7.0
1.5
3.4
5.0
4.4
B. STEEL AND WROUGHT IRON PIPE (STD. WGT.)
Nominal Size:
Inches
Based On Lineal Foot
1/2"
3/4"
1"
1-1/4"
1-1/2"
2"
2-1/2"
3"
4"
5"
6"
.016
.028
.045
.078
.106
.174
.249
.384
.661
1.039
1.501
.132
.231
.375
.648
.883
1.455
2.076
3.205
5.519
8.662
12.510
C. COPPER TUBING (TYPE L)
Nominal Size:
Inches
Based on Lineal Foot
3/8"
1/2"
5/8"
3/4"
1"
1-1/4"
1-1/2"
2"
.007
.012
.018
.025
.043
.065
.092
.161
.063
.101
.151
.210
.357
.544
.770
1.340
D. WATER CONVERSION FACTORS
Lbs. of0 -