My First Fall Steamer...
The Steam Whisperer (Formerly Boilerpro)
Member Posts: 834
This was one up on Chicago's northside...very little space for working near the boiler and anywhere else...so it was a regular process of rotating materials from the boiler room to outside to another storage area. Parking was fun too....being right near a major hospital. On the positive side, I stayed in a nice local hotel that was a short 10 minute walk to the jobsite. I bet I was a bit of a sight coming in every evening covered with rust and debris!
We started out with an evaluation of the system after the owner''s had been dealing with years of uneven heating and high fuel bills. They were looking seriously at taking out all or most of the steam and installing hi velocity heating and cooling. The building is an antebellum structure, probably originally a single family home that was enlarged and converted to a 2 flat in the early 1900's. Beautiful stonework on the exterior and much of the original decorative plaster on the interior. It would have been a crime to knock holes into walls and ceilings to install the ductwork.
When we began digging into the system, we found many of the usual culprits.....undersized main venting, oversized and incorrectly piped steamer, and a 21 foot long cast iron baseboard piped as a two pipe but both supply and return tied directly into the original single pipe steam riser. I guessed that was the case before we even pulled off the baseboard to examine the piping. We also found some extensive attic spaces that were causing very heavy heat losses in the chilliest areas that also had the largely useless baseboard.
Since the boiler was about 40 years old, oversized (320,00 input) and mispiped, the owner decided to replace it with the new (175,000 input) Burnham that was sized to handle some extra radiation that might be installed later for heating another floor. I'll be heading back to install a radiator to replace the baseboard and we'll see how the spaces heat after the insulation and sealing work is done before we install another radiator.
After the system gets some run time and cleaning, the main vents will be upgraded and new adjustable Hoffman 1A''s will get installed to help balance the system. Rebuilding the top of the chimney and installing a stainless liner is in the works too.
Even without a good boiler cleaning, the boiler steamed very nicely with the oversized 3 inch header and system riser. We had it running a good hour and the system heated silently.... a very good sign.
We started out with an evaluation of the system after the owner''s had been dealing with years of uneven heating and high fuel bills. They were looking seriously at taking out all or most of the steam and installing hi velocity heating and cooling. The building is an antebellum structure, probably originally a single family home that was enlarged and converted to a 2 flat in the early 1900's. Beautiful stonework on the exterior and much of the original decorative plaster on the interior. It would have been a crime to knock holes into walls and ceilings to install the ductwork.
When we began digging into the system, we found many of the usual culprits.....undersized main venting, oversized and incorrectly piped steamer, and a 21 foot long cast iron baseboard piped as a two pipe but both supply and return tied directly into the original single pipe steam riser. I guessed that was the case before we even pulled off the baseboard to examine the piping. We also found some extensive attic spaces that were causing very heavy heat losses in the chilliest areas that also had the largely useless baseboard.
Since the boiler was about 40 years old, oversized (320,00 input) and mispiped, the owner decided to replace it with the new (175,000 input) Burnham that was sized to handle some extra radiation that might be installed later for heating another floor. I'll be heading back to install a radiator to replace the baseboard and we'll see how the spaces heat after the insulation and sealing work is done before we install another radiator.
After the system gets some run time and cleaning, the main vents will be upgraded and new adjustable Hoffman 1A''s will get installed to help balance the system. Rebuilding the top of the chimney and installing a stainless liner is in the works too.
Even without a good boiler cleaning, the boiler steamed very nicely with the oversized 3 inch header and system riser. We had it running a good hour and the system heated silently.... a very good sign.
There was an error rendering this rich post.
0
Comments
-
Well done!
did the place have mixed radiation originally? or was that the by product of some well intentioned but dumb alteration during the life of the building..that is a good sign when it can be steamed without noise..thats funny with the hotel thing..they probably thought you were a homeless person showing up at the end of the day..hehegwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
History
One floor appears nearly original, however, the top floor was completely remodeled in what appears to be the 1970's or early 80's and that is when the baseboard was installed. I am largely putting it back to original with just shorter but wider radiators. While there a contractor a couple of houses down came down with some more work on a Noble and ???? Vapor system (Chicago). Took a quick look at the boiler....looked like a 600,000 input Peerless 64 heating about 5,000 sq ft of space with all 2 inch piping around the boiler and only 2 out of 3 risers used, no swing joints and no header.
I think I am here to stay in the Chicago steam market. I have yet to see a single steam boiler installed according to good practice.... even when done by the big, reputable steam outfits in 50 unit buildings.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements