Why aren't pump stations "Pumping Away"?
Comments
-
Pumping Away
A lot of people just haven't caught on yet, old habits die hard. years ago when I was younger a worried customer called, the gas company told him that I piped the boiler all wrong, and I would never be able to get the air out of the system, the customer told me the boiler has never been that quiet since I replaced the boiler, with pumping away piping, but it still took him about 5 years until he was not worried anymore, this situation was repeated last year on another boiler replacement. Doing things different than the norm is always controversial
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Doing things right
should not cause so much controversy.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
pumping toward
The theory is that the PRV and expansion tank are non-isolatable from the heat source (solar panels) and the circulators in these small systems aren't monsters, there is no new fluid to introduce dissolved gasses and any installer who knows their stuff will be eliminating nearly all the air from the system at the get-go.
these systems also typically run at 45 PSI (compared to boiler 12 PSI) and that helps keep the gasses dissolved as well.
not Pumping Away in this case isn't a big deal.
still good practice, and our custom built systems all do that.
karl0 -
Yeah... And ANOTHER thing....
I LOVE Viessmann. I think it is some of the finest equipment to grace the face of the Earth. But....
Why don't they follow the "Pumping Away" standards followed by us North Americaners? Most of their Vitodens drawings don't comply in one way or another.
When Siggy ,Bill Shady and myself and were in Germany touring the Wilo Facilities, I mentioned the PONPC to some of their upper pump engineers, and they looked at me like I was from another planet...
I tried explaining my position to them, but they didn't want to hear it.
Funny how some things don't translate well across the different countries...
The Germans have their way of doing things, and the rest of the world has their way of doing things...
In general, if you are not dealing with a high head pump, it doesn't make a big difference pumping towards the PONPC, other than air binding. If you have a high head pump, with a high pressure drop, it becomes a REAL problem.
METhere was an error rendering this rich post.
0 -
I have the same complaint
I agree...I don't love that we pump into the expansion tank on most solar pump stations.
I think the reason they do it that way is just practical...for the solar system to go to stagnation gracefully in case of a power failure or overtemperature condition, steam has to be able to leave the collector from both supply and return ports and push down to the expansion tank.
For fluid to be able to move to the expansion tank from both collector ports, the expansion tank has to be downstream of any check valves in the system. Since most pump stations have a check valve right by the pump, the expansion tank ends up downstream of the pump by default.
For more information about the importance of expansion tank placement (and sizing) during stagnation, google for the many good articles by 'Hausner and Fink et al' on the topic.
~Fortunat
www.revisionenergy.com0 -
a couple reasons
convenience being one of them.
The "safety group" is a fitting that serves multiple purposes. It has the relief valve, pressure gauge, and expansion tank fitting all in one assembly. The expansion tank and relief valve must be above the isolation valves, should someone turn them off and forget the collector would see extreme pressure in full sun.
That safety group fits right up against the check/ isolation valve assembly.
They also want the expansion tank on the return side so it sees the coolest fluid when running, when located up top like that.
I agree closed loop glycol solar systems should run higher pressures than hydronics.
5 bar, 72 psi is a common fill pressure over there. Notice the relief valves are 6 bar, 87 psi for that reason on solar pump stations. 72 psi keeps the boiling point of the glycol around 320F, to prevent the collectors from flashing to steam under stagnation conditions.
Here is a pic of a triple duty solar valve I cut in half. It shows a gauge well, check valve, and isolation valve. When turned to a 45, the edge of the ball holds the check open so you can drain down the collectors. It can also allow thermosiphoning when held open to serve as over-heat protection, when the owners are gone on vacation.
The other picture shows the safety group mounted above the triple duty valve.
Combining all these functions into two valves, or groups, allows for a small package and the least amount of fittings and connections. It also keeps the cost down also as opposed to all individual components.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
you know
I really love this place.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
Solar Webinars
Hot Rod has done some very good webinars on Solar DHW. They should be available on the Caleffi website. I think he covered this in one of the recent ones.0 -
Duplicate post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements