Threaded flanges leaking
Big Will
Member Posts: 395
We have a job with flanges around the pumps. All the pump flanges and butterfly valves are sealing just fine. The only flanges we cant get to seal are The black iron flanges with nipples in them. two of these mate too a globe check valve and two mate to a Y strainer. We have re set them twice now. We replaced the paper gaskets with neoprene but that did not help. the next thing is to double up the gaskets. I have never had this much trouble with a flange before. The funny thing is the leaks have been out of the bolt holes not the flange face. Any insight would be help full
PS we are using full face gaskets.
PS we are using full face gaskets.
0
Comments
-
try not using full face gaskets.
the extra leverage you get having the bolts outside of the gasket may help draw them shut. Have you checked for cracks or sand holes ( if they are cast iron)in the flanges? How square are they to start with?Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
leaks
Are all your bolts even? the slightest list in the flange, one bolt alot tighter than the other may cause leaking,0 -
Nipple depth
Any chance the nipples extended beyond the flange face when tightening and are preventing you from fully making up the flanges?0 -
mis-alignment?
they need to be square to one another the gasket will not make up for crooked alignment.
What about expansion and contraction movement? excessive pressure, maybe not enough expansion tank capacity?
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Ye haw
SO we went to steel ring gaskets between the Y strainer and flange easy money. However the other side of the pump is a globe style silent check valve. these have two screws in the face of the flange that hold the brass check in place. those screws line up with the flange bolt holes. It leaves about an 1/8th of an inch. between the flange bolt holes and the set screw. Could not get it to stop leaking out the bolt holes. We assembled the whole thing and blank flanged the ends. Ended up using two neoprene gaskets and getting a good seal at 125 Psi in a immersion test. I hate having to use two gaskets it feel like defeat. However it has held for two days now. With all of the fighting with it last week I am calling it done. I will say I have never had problems like this with flanges its been very frustrating0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 932 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements