Navien Heat Exchanger Failure
salmonhunter71
Member Posts: 11
I am having issues with 2-Navien's. One is doing half of the domestic load only, the other is heating a basement slab with a heatbox & doing domestic for the other half of the house. The first units went out with bad heat exchangers after 6-mos. Now after replacing those first 2 in Feb of 2010, the second set is leaking again.
Both have recircs 210ANG,240ANG the 240ANG has a external pump because it is tied into a heat box & was installed as per Navien.
I had the water checked by a third party, and it came back well within the acceptable tolerances. Electrician checked for leakage of power or poor grounding, checked out good.
Now this is where it gets odd, the 1/2 proflo brass ball valve that isolates the recirc has developed a tiny pin-hole , healing itself as the deposit seals it up.
The Webstones feel a little crunchy.
I thought I would do a little professional testing of my own on my finger and taste the mineral deposit to see if was salty or what. It was like licking a 9-volt, very bitter.
So, Navien jumped the gun & said it was the water, I said prove it. They have yet to tell me what I need to look for in the water. This is a new issue for them? Basically, I need to know what the issue is before we move forward.
Any comment's or suggestions are welcome.
Both have recircs 210ANG,240ANG the 240ANG has a external pump because it is tied into a heat box & was installed as per Navien.
I had the water checked by a third party, and it came back well within the acceptable tolerances. Electrician checked for leakage of power or poor grounding, checked out good.
Now this is where it gets odd, the 1/2 proflo brass ball valve that isolates the recirc has developed a tiny pin-hole , healing itself as the deposit seals it up.
The Webstones feel a little crunchy.
I thought I would do a little professional testing of my own on my finger and taste the mineral deposit to see if was salty or what. It was like licking a 9-volt, very bitter.
So, Navien jumped the gun & said it was the water, I said prove it. They have yet to tell me what I need to look for in the water. This is a new issue for them? Basically, I need to know what the issue is before we move forward.
Any comment's or suggestions are welcome.
0
Comments
-
What pump?
Explain why the 240ANG would have an external pump when the pump in the heat box creates the flow through the Navien unit to make it fire?
There should be no extra pump or circ between the heat box/Navien connections
Did you add one (not shown in instructions) and by doing so double stack the units resulting in excessive head and flow?
http://www.navienamerica.com/PDS/ftp/HeatingBox/HeatingBoxTrainingManual.pdf0 -
unscientific response
but whenever I hear "pinhole leaks" and freshwater systems, I think electrolysis immediately.
is it possible that you have a grounding issue?Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
Did you check
The waters ph. I recently was on a "problem" job, not navien, that had a water ph of 4. That is the ph of coca cola, or Pepsi even.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements