broomell system
mikeyone
Member Posts: 3
where do we install the receiver?, the old lit says water line of boiler to water line of receiver?,but have seen pics on this site where it is not.
also do we need to install a hartford loop on this type of system?
also do we need to install a hartford loop on this type of system?
0
Comments
-
perhaps this will help.
look i think at page 5.. this info is from Dan's library section.. http://www.heatinghelp.com/article/163/Older-Steam-Heating-Systems/1363/Broomell-Specifications-from-1924
and if its a gravity return you need to install a hartford loop..if its a pumped return its not required unless the local authority desires it.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
broomell
thanks,gerry I agree just trying to reassure ourselves before replacing this boiler,seems some of the pics on this site don't agree.trying to avoid any mistakes0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements