Oil burner rumbling on start up and end
Marilyn_4
Member Posts: 26
Beckett burner with a L 1 air tabulator on the nozzle assembly.3 section Lennox boiler. 1 pipe top feed to burner.
It started as a normal yearly cleaning. Changed oil filter, A strainer, .75 70A nozzle. Removed smoke stack, vacuumed chimney and boiler.
Started her up fine. Upon shut off there was additional oil from nozzle that caused a rumble in the boiler and smoke pipe.
Took out the nozzle to check again and noticed the air tabulator was coming apart. Replaced it with a new L 1. Same thing...extra oil after shut off and rumbling.
Smoke test was clean. Draft over flame was -.02 breach -.04
I moved the nozzle assembly forward which stopped the extra oil and rumbling but then I had a bad smoke reading. Draft over flame was +.03 -.04 breach.
I'm going to call Beckett today to get the right settings.
Any ideas why this would be happening and what I can do to stop it before calling Beckett?
Thanks,
Maz
It started as a normal yearly cleaning. Changed oil filter, A strainer, .75 70A nozzle. Removed smoke stack, vacuumed chimney and boiler.
Started her up fine. Upon shut off there was additional oil from nozzle that caused a rumble in the boiler and smoke pipe.
Took out the nozzle to check again and noticed the air tabulator was coming apart. Replaced it with a new L 1. Same thing...extra oil after shut off and rumbling.
Smoke test was clean. Draft over flame was -.02 breach -.04
I moved the nozzle assembly forward which stopped the extra oil and rumbling but then I had a bad smoke reading. Draft over flame was +.03 -.04 breach.
I'm going to call Beckett today to get the right settings.
Any ideas why this would be happening and what I can do to stop it before calling Beckett?
Thanks,
Maz
0
Comments
-
Maz
I have used these with good success on different rumbling applications.
http://www.delavaninc.com/protek.htm
They screw-on in place of the nozzle filter and are sized according to your pumps pressure setting.0 -
Dave
These are nozzles that you replace with the Typical Delvan nozzle?0 -
Maz
Yes they are, look around the Delavan site for more info.
I had a PDF but it will not load,,,, aaarrrggg!0 -
air
That will cause problems. Where, if any, is the filter located? Vacuum test?0 -
Agreed bill,
but this will likely solve-it, try this link. ;-)
http://www.delavaninc.com/pdf/protek_sheet.pdf0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements