Which way to go?
Techman
Member Posts: 2,144
I have a customer w/ a lobster tank that has an undersized condensing unit,but, only undersized during this summers heat wave.I also have a same size cond unit minus the compressor, so ,I am thinking of hooking up the cond coil/ cond fan motor /reciever tank in conjuction w/ the undresized cond unit. So, should it be in series or parallel ? And should cond coil #2 w/ or w/o recieves tank be hooked up before/after cond unit #1 reciever tank ?Think away and advise away! I'm all ears! Not ALL ears,that is, I do have a few other parts!Thanks!
0
Comments
-
my opinion is
pipe the second condenser in parallel with the first and put a solenoid valve on it, controlled by a hi pressure switch to cycle it on when you need it. Receiver, after consulting a Sporlan Cold War paper, March 2007, all receivers should be in series. You probably remember the old Copeland condensers with dual receivers
Let us know what you did?
Don in MO0 -
Receiver in Series
As Don said, all receivers should be in series. Otherwise, there will be no flow through it.
Reminds me of a consultation I was called on a few years back. Fellow had just replaced the condensing unit on a commercial walk-in refrigerator. The low side kept pulling into a vacuum, no matter how much refrigerant he forced into the system. He gave me a call and I headed over to take a look at it.
He installed the new condensing unit just fine. Only problem was that the new condensing unit had a receiver and the system was operating with a cap tube.
Personally, I would attack it this way. Install the second condenser coil in parallel with the first, but I would leave the second receiver out of the picture altogether. As Don mentioned, install a solenoid in series with the second coil and control it by head pressure. As the head pressure rises, the solenoid opens, adding the second condenser to the mix.
Have fun and let us know how it works out!There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements