run capacitor

marsco
Member Posts: 6
what makes the common side of a duel capacitor burn off at the terminal. the unit also has a potential relay and a start cap. the cap only a week.
0
Comments
-
burning
the most common cause is a loose connection.If the crimp connector can be "wiggled" it is loose .If the crimp connector has "metal fatigue" it is loose. A loose connection is a hot connection and then it's "burn ,baby, burn"0